The cable to the socket is indeed 2.5mm. All of the breakers for the sockets are 32A so you've got a dangerous situation there.
The cables look relatively new so I take that the cables for the sockets were changed as part of the rewire?
Carefully, remove the case of the consumer unit with the power off and show us a picture of the cable leaving the MCB for the sockets.
Or get a multimeter, remove the socket and measure the continuity from all of the conductors behind the socket (L to L N to N CPC to CPC) you should get a beep. Circuit should be powered off. I prefer this method.
The cables look relatively new so I take that the cables for the sockets were changed as part of the rewire?
Carefully, remove the case of the consumer unit with the power off and show us a picture of the cable leaving the MCB for the sockets.
Or get a multimeter, remove the socket and measure the continuity from all of the conductors behind the socket (L to L N to N CPC to CPC) you should get a beep. Circuit should be powered off. I prefer this method.