Not at all. Both radials and rings are acceptable, but radials seem to be becoming increasingly more popular.Really 4mm radial? What would the average electrician install? I know the rational behind our UK ring circuits but I believed that was the required standard.
Were it not for the dispensation (which involves a certain amount of guessing about how the circuit is likely to be used) the UK ring final circuit would not be compliant with the regulations. Such a circuit is not acceptable in many countries outside of the UK
As above, radial circuits are at least as acceptable as rings, provided the correct size cable is used in relation to the rating of the breaker protecting it. If 2.5mm² cable is used, the breaker would usually be 20A, perhaps 25A, but with 4mm² cable one can usually use a 32A one. The rating of the breaker obviously defines the theoretical maximum total load that should be supplied to the circuit.So I can leave my other circuits which I believe are radial? That makes things a bit simpler.