I think the installer has just used what breakers the cu came with. They didn’t tend to come with b20
Would also explain the spare mcbs
Would also explain the spare mcbs

I’ve just ripped all the tiles off.Wylex make 25amp breakers - could be your best bet.
Crap plastering, btw.
What a confusing question from a supposed expertHow do we know it is 2.5mm²?
UrbanGreen: Are the Line and Neutral wires stranded or just a single core?

UrbanGreen did not seem to have a problem with it.What a confusing question from a supposed expert

With power off, removing the two brown wires, there should be continuity between them. The same applies to the blue wires. And the two earth wires, if no continuity, likely it is a radial. It could also be a donor socket for a spur, but unlikely.
and other than when having a shower, or recharging batteries the power used rarely exceeds 4 kW, so if all my B32 RCBO's were changed to B20 RCBO's it is unlikely they would ever trip. That would seem to be the easy way forward.Not doing a photo of that now. I’ve removed all of the wiring in the kitchen and will get a fresh ring installed. It seems to have been a radial with some sort of ring tied into it. There’s definitely only a single cable going into all of the socket circuits. Three socket circuits and multi core cable going into them so I’m guessing they are 4mm2 radial circuits as opposed to my assumption that I had three ring circuits. What period do radial circuits come from? How is a householder supposed to know what he has got?@UrbanGreen Waiting patiently for a picture of the cable(s) leaving the breakers for the sockets.
Very useful information.View attachment 369810 With power off, removing the two brown wires, there should be continuity between them. The same applies to the blue wires. And the two earth wires, if no continuity, likely it is a radial. It could also be a donor socket for a spur, but unlikely.
The BS 7671 came out in 1992, from that point electricians were encouraged to take an exam to show they could read the book, 2001 was the next major change, followed by 2008 and 2018. By 2001 I would have thought no re-wire was completed without producing paperwork, and by 2004 the Part P law forced the production of paperwork for re-wires.
The rules (other than rental property) say an EICR (was called a PIR) should be done every 10 years or change of occupant, which ever is shortest. We are, of course, assuming a real inspection and test, and not a drive by. I note my house buyer's report included an EICR, however not really up to standard, he noted a disused fuse box in the ceiling space, it was not disused.
My house generates a display of the power used, View attachment 369820 and other than when having a shower, or recharging batteries the power used rarely exceeds 4 kW, so if all my B32 RCBO's were changed to B20 RCBO's it is unlikely they would ever trip. That would seem to be the easy way forward.
What a confusing question from a supposed expert
It obviously depends upon the topography/layout, but 4mm² T+E is a fair bit less than double the price of 2.5mm².Nothing wrong with a 4mm radial. Ideal for a kitchen. 2.5mm cable for ring could be cheaper
Really 4mm radial? What would the average electrician install? I know the rational behind our UK ring circuits but I believed that was the required standard. So I can leave my other circuits which I believe are radial? That makes things a bit simpler. As my feed to the kitchen is a 4mm I could just have it wired as a radial. In 4mm obviously.Nothing wrong with a 4mm radial. Ideal for a kitchen.
2.5mm cable for ring could be cheaper