Shower Cable Rating - Slightly Different!

Discussion in 'Electrics UK' started by Mirez, 13 Aug 2012.

  1. Mirez

    Mirez

    Joined:
    10 Jan 2010
    Messages:
    12
    Thanks Received:
    0
    Location:
    Wiltshire
    Country:
    United Kingdom
    Hi Guys, I've got an 8.5Kw shower which I need to replace - all good shouldn't be a problem (ha-ha)... I looked at the breaker and its 40amp, checked the cable exiting the box and its 10mm. Great, a 9.5Kw shower will be nice upgrade.

    Now the problem is I've just come to fit the thing and removing the old shower reveals a 6mm cable, further investigation reveals that it changed from a 10mm to a 6mm at the isolator pull cord.

    So, firstly I'm fairly happy that I can't fit a 9.5Kw using this setup as 6mm isn't sufficient - correct?

    Secondly, to my mind I need to replace this (2ish meter) section of 6mm as this current set-up isn't acceptable anyway (as the cable down the line is a lower rating then the MCB) - again correct?

    Cheers!
     
  2. Sponsored Links
  3. wingcoax

    wingcoax

    Joined:
    1 Mar 2009
    Messages:
    1,948
    Thanks Received:
    158
    Location:
    Blackpool
    Country:
    United Kingdom
    Replace the cable and make sure all connections are tight. You are lucky, in that i have found cables the" other way round" even to the extent of 2.5mm changing to 6.00mm.
     
  4. Risteard

    Risteard

    Joined:
    18 Jun 2010
    Messages:
    2,034
    Thanks Received:
    141
    Location:
    Derry, Ireland
    Country:
    Ireland
    Not necessarily, as long as it provides adequate fault protection (which could be proven by calculation). Overload protection won't be required for the shower as it is a fixed load and therefore cannot overload.
     
  5. PrenticeBoyofDerry

    PrenticeBoyofDerry

    Joined:
    30 Jun 2009
    Messages:
    21,628
    Thanks Received:
    2,383
    Location:
    Londonderry
    Country:
    United Kingdom
    I personally feel although it's a borderline case as far as device and load ratings, that I would replace the 6mm cable for 10mm. The reason being that you have found/noticed this, maybe if you leave it as is, sometime in the not so distant future someone may decide to upgrade shower to 10.5kW say, look at the 10mm think that's great and not notice the 6mm (or chose to ignore it once purchased new shower)!
     
  6. Mirez

    Mirez

    Joined:
    10 Jan 2010
    Messages:
    12
    Thanks Received:
    0
    Location:
    Wiltshire
    Country:
    United Kingdom
    Thanks guys, I think that's exactly what I will do - I can keep my 9.5Kw shower then lol. Cheers!
     
  7. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    33,623
    Thanks Received:
    3,676
    Location:
    Retired to:
    Country:
    Portugal
    If the manufacturer states 9.5kW @ 240V AND the 6mm² cable is not in thermal insulation then all is perfectly acceptable.

    Perhaps the 10mm² was installed because of insulation but no need to replace the 6mm²

    No, not correct. It's fine (with the above insulation proviso).


    No such thing as borderline. It either complies or it doesn't.

    That'll be their fault. Mirez noticed it.

    No need to allow for idiots in the future.
     
  8. Sponsored Links
  9. westie101

    westie101

    Joined:
    3 Jan 2011
    Messages:
    2,497
    Thanks Received:
    313
    Location:
    Cumberland
    Country:
    United Kingdom
    Though not really required as some say, I would suggest that it comes under the heading of good practice and would strongly agree with the OP that it is the right thing to do.
     
  10. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    33,623
    Thanks Received:
    3,676
    Location:
    Retired to:
    Country:
    Portugal
    Nope, no need.

    It could have been designed like that, properly.
     
  11. PrenticeBoyofDerry

    PrenticeBoyofDerry

    Joined:
    30 Jun 2009
    Messages:
    21,628
    Thanks Received:
    2,383
    Location:
    Londonderry
    Country:
    United Kingdom
    Fair enough
    As stated, my personal opinion on the best/most sensible solution.
    No need to also ignore potential idiotic behaviour in the future or make provisions for upgrades.
     
  12. mfarrow

    mfarrow

    Joined:
    2 Nov 2009
    Messages:
    2,126
    Thanks Received:
    243
    Location:
    Warwickshire
    Country:
    United Kingdom
    If we future proof for every person's what-ifs then copper prices would be double what they are at the moment.
     
  13. ebee

    ebee

    Joined:
    14 Aug 2005
    Messages:
    1,711
    Thanks Received:
    29
    Location:
    Lancashire
    Country:
    United Kingdom
    Copper prices are not what they are at the moment anyway- they are double.

    Did we mention Part P here?

    :D
     
  14. PrenticeBoyofDerry

    PrenticeBoyofDerry

    Joined:
    30 Jun 2009
    Messages:
    21,628
    Thanks Received:
    2,383
    Location:
    Londonderry
    Country:
    United Kingdom
    They can then consider the copper within the walls and ceilings as an investment!
     
  15. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page