Spark from immersion heater switch

Discussion in 'Electrics UK' started by DiyNutJob, 26 Nov 2021.

  1. DiyNutJob

    DiyNutJob

    Joined:
    29 Aug 2011
    Messages:
    349
    Thanks Received:
    19
    Location:
    London
    Country:
    United Kingdom
    I had an immersion heater switch that sparked intermittently. So I replaced it with a new one. The new one sparks even more when switching off. The new one from wickes is ASTA approved, etc.

    I understand the why's of the spark. But, I still prefer no spark. Is there such a thing as a non-sparking switch? Another switch at that location was overheated once, and burnt out. Is that an indication there is something wrong with the immersion heater?
     
    Last edited: 26 Nov 2021
  2. Sponsored Links
  3. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    9,265
    Thanks Received:
    1,182
    Location:
    Dorset
    Country:
    United Kingdom
    If the switch is a good quality, and wired correctly, safely, with sound connections, you can still get 'arcing', where you get a small flash showing round the switch itself.

    I do not know of a switch that is guaranteed not to do this.
     
    • Thanks Thanks x 1
  4. RandomGrinch

    RandomGrinch

    Joined:
    15 Jun 2021
    Messages:
    1,963
    Thanks Received:
    452
    Location:
    Wales
    Country:
    United Kingdom
    Hi,

    This may be slightly over the top, but could it be worth considering a 2-pole isolator?
    Something like this:

    19b9779d-9e66-4905-a651-058e873f8aff_704x832.jpg

    https://www.sparkswarehouse.com/col...ducts/bg-cprsd220-rotary-isolator-2p-20a-ip65

    They are significantly 'beefier' than a standard switch, and easy to turn on and off.

    Edit: although it wouldn't be a straight swap, cable glands and a fused outlet would have to be considered.

    The problem is, when arcing occurs, the switch contacts are damaged. This causes higher resistance within the contacts, eventually causing even more heat damage.
    A destructive feedback cycle!

    ...and yes, it is possible that there is something wrong with the immersion!
     
    Last edited: 26 Nov 2021
  5. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    7,599
    Thanks Received:
    593
    Location:
    London
    Country:
    United Kingdom
    An immersion heater typically takes 3kW and when breaking such a load you will get a spark and switch wear. Nothing wrong with the immersion heater, just laws of physics.
     
    • Like Like x 2
    • Thanks Thanks x 1
  6. DiyNutJob

    DiyNutJob

    Joined:
    29 Aug 2011
    Messages:
    349
    Thanks Received:
    19
    Location:
    London
    Country:
    United Kingdom
    My understanding is that arc'ing always happens with conventional switches. I am just curious if there are any non-conventional switches for domestic use. So, there aren't.
     
    Last edited: 26 Nov 2021
  7. DiyNutJob

    DiyNutJob

    Joined:
    29 Aug 2011
    Messages:
    349
    Thanks Received:
    19
    Location:
    London
    Country:
    United Kingdom
    You are pulling my leg. The heater is protected by a fuse at the consumer unit. There's probably nothing wrong with it. When I asked the question, I was still thinking the broken heater overloading the switch.

    Now I am thinking the heater is overloading the worn switch caused by arcing. So the heater is OK, but the worn switch has to be replaced or the diminishing contact will cause a melt down.
     
    Last edited: 26 Nov 2021
  8. RandomGrinch

    RandomGrinch

    Joined:
    15 Jun 2021
    Messages:
    1,963
    Thanks Received:
    452
    Location:
    Wales
    Country:
    United Kingdom
    Yes, not a conventional switch; but again as I said, there is nothing wrong with using a small industrial switch, that won't have issues with arcing, in a domestic environment.
     
  9. Harry Bloomfield

    Harry Bloomfield

    Joined:
    30 Dec 2018
    Messages:
    10,634
    Thanks Received:
    1,425
    Country:
    United Kingdom
    They always do spark/arc, but the amount can vary depending on when during the 50Hz cycle the switch is triggered - worse near one of the voltage peaks. If the arc persists longer than a fraction of a second, or it can be triggered by touching the switch - that suggests the switch may be faulty or that the switch operator is using the switch wrongly. A switch should be flicked quickly with a finger tip, rather than gripped and moved gently.

    Arc visibility can appear to be worse in thin or white coloured switches, plus when it is dark - brown or black plastic hides the arc better.
     
    • Like Like x 3
  10. Sponsored Links
  11. RandomGrinch

    RandomGrinch

    Joined:
    15 Jun 2021
    Messages:
    1,963
    Thanks Received:
    452
    Location:
    Wales
    Country:
    United Kingdom
    Well anythings possible! ;)

    It will take a good while for a switch to be destroyed by arcing, so don't panic! But, yes, that could be the failure mechanism :)
     
  12. DiyNutJob

    DiyNutJob

    Joined:
    29 Aug 2011
    Messages:
    349
    Thanks Received:
    19
    Location:
    London
    Country:
    United Kingdom
    Something that fits directly will be OK. We are not all builders and electricians. It would be too involved to set it up. They should make a domestic version that are more domestic looking.
     
    • Like Like x 1
  13. DiyNutJob

    DiyNutJob

    Joined:
    29 Aug 2011
    Messages:
    349
    Thanks Received:
    19
    Location:
    London
    Country:
    United Kingdom
    Both the new and old switches are conventional white. The new one sparks more, giving the rocker piece a surround-light kind of look.
     
  14. terryplumb

    terryplumb

    Joined:
    8 May 2017
    Messages:
    6,639
    Thanks Received:
    1,406
    Country:
    United Kingdom
    What type of switch do you currently have ,is it double pole ? Rated at 20 amp ?
     
  15. DiyNutJob

    DiyNutJob

    Joined:
    29 Aug 2011
    Messages:
    349
    Thanks Received:
    19
    Location:
    London
    Country:
    United Kingdom
    Are you quite sure? Maybe cheap switches use cheap metals and wear out after 5 switches. If they do a four-pronged iridium version, that would be OK. Those are known to last 100k miles on the car.
     
    Last edited: 26 Nov 2021
  16. Harry Bloomfield

    Harry Bloomfield

    Joined:
    30 Dec 2018
    Messages:
    10,634
    Thanks Received:
    1,425
    Country:
    United Kingdom
    When it is turned on and you feel the switch, does it feel warm? If not, just ignore the arc - assuming as above it is marked 20amps.
     