No.I agree with bernardgreen, if the stainless will be forming part of the enclosure for electrical accessories it will be an exposed conductive part.
Exposed conductive parts must be bonded.
Exposed-conductive-parts must be earthed, not bonded.
HI Mark,
Are you going to post a couple of pics when its finished?
Sounds like it will be nice.
No.
isn't there a test to verify whether any exposed metalwork or similar could be defined as an ECP?
(thinks >23000ohm)![]()
I want to call it what it is, and I want everybody to call it what it is.Bonded back to the MET via the CPC, or earthed. Whatever you want to call it.
No.No.
How about both ?
The problem with that argument is that it will lead you to bonding all sorts of metal all over the house..Earthing a metal surface via the CPC in the cable is OK until the ( extreme ) fault of cable damage leaving the CPC to the surface in contact with the live conductor in the cable and no longer connected to the earth at the CU. At the time the damage is done the RCD and MCB may trip. They are reset but the fault remains with the ""earthed "" metal now live. Bonding to other earthed items would prevent the RCD and / or MCB being reset. Or if the other surfaces were not earthed bonding would reduce the risk of shock from two metal surfaces in that room being at different potentials.
No - it won't change what is or is not an exposed-conductive-part or an extraneous-conductive-part into one which is not or is.But the fault that occurs after the test may at a later date change the status of the exposed metal work.