If you do a bit of integration on a sine curve, what's the area under it?[when you say 'under the trace', I presume you mean 'between the trace and the V=0 line] That would give the mean, not the RMS, wouldn't it?
Kind Regards, John
If you do a bit of integration on a sine curve, what's the area under it?[when you say 'under the trace', I presume you mean 'between the trace and the V=0 line] That would give the mean, not the RMS, wouldn't it?
Kind Regards, John
From their Website
EGS 5
–
Supply voltage (Regulation 15)
If you inform us that the electricity to your
property is outside the permitted voltage
range, we will contact you and arrange a visit
to your property within seven working days,
or, if a visit is not necessary, we will provide
a written response within five working days.
If we fail these timescales we will arrange
for you to receive £22.
£22? What a bizarrely arbitrary figure... I wonder how they arrived at that.
I did a search of UK Power Networks site and couldn't find any info on supply specification. Maybe I was barking up the wrong search-term tree. Would you provide a link for this please? I can quote it back to them
To be clear for the OP, from recent discussions here ISTR that the requirement is that the voltage remains within than range for 95% of the time, and that the figures looked at are averages over a period of time (was it 30 mins?). Is that correct?Google ESQCR, but it is 230V +10/-6% at the DNO terminalsI did a search of UK Power Networks site and couldn't find any info on supply specification. Maybe I was barking up the wrong search-term tree. Would you provide a link for this please? I can quote it back to them
Missed this one last night ... the area under (or definite integral of) any voltage-time curve between two points in time will surely give you a measure of the mean voltage during that period multiplied by the duration of the period? Hence, if you divide thatarea by the durationof the period, you will get the mean voltage over that period. That statement obviously needs a little 'pedantic tweaking' if the curve has both positive and negative parts, but it is true, say, for one positive half-cycle of a sine wave.If you do a bit of integration on a sine curve, what's the area under it?[when you say 'under the trace', I presume you mean 'between the trace and the V=0 line] That would give the mean, not the RMS, wouldn't it?
To be clear for the OP, from recent discussions here ISTR that the requirement is that the voltage remains within than range for 95% of the time, and that the figures looked at are averages over a period of time (was it 30 mins?). Is that correct?
Thanks (on behalf of the OP).95% measured over 7 days and averaged at 10 minute reading intervals, what it does is take a lot of the very short duration spikes out.