Am I right in thinking that a bathroom with only a pull cord lightswitch (and centre light) DOES NOT REQUIRE any further bonding. The bonding in effect being supplied by the protective conductors feeding the switch and light point.
http://www.iee.org/Forums/forum/messageview.cfm?catid=205&threadid=5562&enterthread=ysteveg1957 said:Am I right in thinking that a bathroom with only a pull cord lightswitch (and centre light) DOES NOT REQUIRE any further bonding. The bonding in effect being supplied by the protective conductors feeding the switch and light point.
No, supplementary bonding is still required between any extraneous metal hot water, cold water and radiator pipes. The lights themselves should not be bonded but should be fed from an approved (BS EN 60742) transformer . (SELV)DIYchallenged said:Apologies for hijacking this thread, but it is relevent ............
I have no mains power in my bathroom - no electric shower, shaver socket or heater, and the lights are 12V downlighters. Am I right in assuming that no bonding is required?
ban-all-sheds said:No - not "all exposed metalwork", only extraneous-conductive-parts.
You'll actually make things worse if you go bonding things just because they are metal, and exposed, if they aren't in any way connected to earth...
trouble with this attitude is that if a person does manage to touch something live then earthed metalwork is dangerous to themstevesey said:However I generally prefer the idea that all exposed metalwork is bonded and earthed (within practical limits of course) so that if a fault occurs (within the bathroom) the supply will trip. For example if my recharging shaver makes the wire shelf rack live, I'd rather the supply tripped than risk someone touching the rack and the cold tap. Largely theoretical of course, as I don't have a wire rack in the bathroom and if I did I probably wouldn't consider it practial to bond it!
I prefer to think of it as going for a very important level of accuracy..stevesey said:Going for the detail as ever BAS!
You really aren't that clear on the definition of an extraneous-conductive-part, are you...As far as the regulations go you are of course correct, "extraneous-conductive-parts" meaning any part that extends outside the room (and could therefore introduce a potential into the room because of an external fault).
You may prefer what you like - the regulations take a different view, and I cannot see how deliberately making something into an extraneous-conductive-part when it wasn't before is a safety measure.However I generally prefer the idea that all exposed metalwork is bonded and earthed (within practical limits of course)
ban-all-sheds said:I prefer to think of it as going for a very important level of accuracy..stevesey said:Going for the detail as ever BAS!
securespark said:ban-all-sheds said:I prefer to think of it as going for a very important level of accuracy..stevesey said:Going for the detail as ever BAS!
I have to agree 100% with Ban here.
If you are going to give/receive information, it mas as well be accurate, especially so where electricity and bathrooms are involved, don't you think?