Found this one today:
The pic isn't great but the installer earthed the swa that runs down the garden to a greenhouse by taking about 1/4 of the armour, twisted and insulated, to the earth terminal.
He also covered it in black insulation tape, probably to hide the evidence .
I will certainly be redoing this, probably using an adjacent adaptable box.
However, although I thought (and still think) it was crap and should be ripped out, I then wondered if could be argued that it was 'compliant'.
From tables, the equivalent csa of that armouring would be 15mm, so even 1/4 or 1/5th of it would still be greater than 1.5mm.
Add to this that its a TT supply with a Ze of 20Ω at the distribution board, and I guess it becomes more a question of quality of workmanship rather than safety? I haven't tested it at the remote end but assuming that Zs was less than 30Ω then would that make it compliant?
The circuit is off at the moment anyway and the cable may have to be replaced because of voltage drop as the greenhouse is some way down the garden and I haven't got round to doing the calcs yet (busy sorting out all the other nice surprises).
However, would be interested to hear more experienced views.
Gavin
The pic isn't great but the installer earthed the swa that runs down the garden to a greenhouse by taking about 1/4 of the armour, twisted and insulated, to the earth terminal.
He also covered it in black insulation tape, probably to hide the evidence .
I will certainly be redoing this, probably using an adjacent adaptable box.
However, although I thought (and still think) it was crap and should be ripped out, I then wondered if could be argued that it was 'compliant'.
From tables, the equivalent csa of that armouring would be 15mm, so even 1/4 or 1/5th of it would still be greater than 1.5mm.
Add to this that its a TT supply with a Ze of 20Ω at the distribution board, and I guess it becomes more a question of quality of workmanship rather than safety? I haven't tested it at the remote end but assuming that Zs was less than 30Ω then would that make it compliant?
The circuit is off at the moment anyway and the cable may have to be replaced because of voltage drop as the greenhouse is some way down the garden and I haven't got round to doing the calcs yet (busy sorting out all the other nice surprises).
However, would be interested to hear more experienced views.