    Hi there, I'm upgrading my thermostat from salus rt310 to rt310rf, and want to make sure my wiring is correct. The Thermostat is connected to a 3 channel programmer.

    Inside the rt310 are 2 wires brown (live connected to COM), and a grey connected to NO. There is also an unconnected black wire inside - I wonder what that is for?

    Could someone have a look at schematic and confirm the correct wiring I need to follow.
    I think in the receiver I connect brown to L and COM, the grey to NO, would the black wire go to N?
     

    Attached Files:

  2. Sponsored Links
  3. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,086
    Thanks Received:
    4,161
    Location:
    Retired to:
    Country:
    Portugal
    That is correct, BUT you will first need to make sure the Black is connected to neutral at the other end.
     
    • Like Like x 1
  4. Zooropa68

    Zooropa68

    Joined:
    12 Sep 2021
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks, so if I get my multimeter and confirm black and grey are connected on continuity check then I'm good to go?
     
  5. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,086
    Thanks Received:
    4,161
    Location:
    Retired to:
    Country:
    Portugal
    No. You must check the other end of the cable and connect the Black to a supply Neutral.
     
    • Like Like x 1
  6. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    9,817
    Thanks Received:
    1,962
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    One of those is a battery powered wired thermostat, the other is a battery powered wireless thermostat with a 230V wired receiver unit.
    The receiver is intended to be located out of sight, typically next to the boiler or similar. Not where an old thermostat was previously located.

    The existing thermostat will only have power when the programmer is on.
    Installing the receiver unit there will not work, as it requires power permanently.
     
  7. Zooropa68

    Zooropa68

    Joined:
    12 Sep 2021
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    The brown wire in it measures 240v

    The reason I want to change thermostat, is because it is in a large hallway next to a frontdoor, the temperature in hall is always lower than the living room and it can heat up too much. I want to put Thermostat in living room and have receiver in position of old Thermostat
     
    Last edited: 12 Sep 2021
  8. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    9,817
    Thanks Received:
    1,962
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    The old thermostat switches 230V.
    It is not powered by 230V, as it doesn't have a neutral connection, and most obviously it also has 2 AA batteries inside.

    If you connect the unused black to neutral wherever the other end is, and install the receiver where the old thermostat was, and use the brown for L and the black for N and the grey for switched L, the receiver will have power when the programmer is set for heating on.

    When the programmer is off the receiver will have no power. The battery thermostat will then waste the batteries away trying to contact the unpowered receiver.
    End result - new batteries required every month.

    Given it's a Salus, it will probably unpair itself at regular intervals as well, perhaps every time the programmer switches the heating off.
     
    • Thanks Thanks x 1
  9. Sponsored Links
  10. Zooropa68

    Zooropa68

    Joined:
    12 Sep 2021
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    I was hoping this would be straightforward, but maybe not.

    I guess I could power the receiver via a separate external mains cable live and neutral, and just use same 2 wires which are for original thermostat.
     
  11. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    9,817
    Thanks Received:
    1,962
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    Only if that external cable is connected to the same 3A FCU that supplies the rest of the heating controls.
     
  12. Zooropa68

    Zooropa68

    Joined:
    12 Sep 2021
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    Is that the regulations?
     
  13. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,086
    Thanks Received:
    4,161
    Location:
    Retired to:
    Country:
    Portugal
    I am sorry I did not realise the limitations of the device. I assumed the thermostat was a timer as well.

    All you have to do is install the receiver near the programmer, wiring centre or boiler; wherever the appropriate wiring is.
     
    • Like Like x 1
  14. Zooropa68

    Zooropa68

    Joined:
    12 Sep 2021
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
  15. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,453
    Thanks Received:
    2,116
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Yes it is.

    consider a plumber, perhaps, working on the heating system. He/she would expect that turning off the boiler at its isolation switch would disconnect power from the whole of the system.
     