What size is the wire from consumer unit to cooker switch

The manual for the cooker
@Macmhuirich is yours dual fuel or all electric ??
The spec for dual fuel says - as below - 7.4kW. You don’t need 10mm for that.
IMG_5280.jpeg
 
But the spec at the end of that document says 16.24kW!
Yes, not that they will all be on together.

As Rodders worked out in post 25:

Which by my sums would be nearly 71 Amps - but allowing for diversity is 10A + 0.3 x 61 A = 10+18.3 = 28.3 A... so within a B32 MCB rating. Unless the cooker is fed from a switch with a13A socket; in which case the + 5A extra tips it over.

So, don't have a socket.

You either believe in diversity or you don't.

Still happy with 4mm?
Yes, I don't use BS3036 30A fuses any more.
 
You either believe in diversity or you don't.
Having suffered due to and repaired the damage caused by diversity on several occasions... no I don't agree to the extent that others religiously adhere to the regs.
MI's are usually a far better guide.
 