Thanks for all your replies I very much appreciate it . I’m fitting a new range master range cooker which the book states must be wired with 10mm2 cable max . I measured mains wire and it’s like 4mm and on a 32A RCD at consumer unit . I would imagine you can’t use a 10mm cable to a 4mm one and the lad that delivered it says it has to be on a 45A RCD at consumer unit with the 10mm . Thanks again
Thanks for all your replies I very much appreciate it . I’m fitting a new range master range cooker which the book states must be wired with 10mm2 cable max
The 10 sq mm is merely the biggest that the terminals accept... removing the link supplied reduces the capacity to 6 sq mm for a 3-phase 400V installation (weirdly the manual says the same earth terminal capacity reduces to 6 sw mm, too!).
From Page 42:
Maximum total electrical load at 230 V (approximate total including hob, oven lights, oven fan, etc.): 16.24 kW
Which by my sums would be nearly 71 Amps - but allowing for diversity is 10A + 0.3 x 61 A = 10+18.3 = 28.3 A... so within a B32 MCB rating. Unless the cooker is fed from a switch with a13A socket; in which case the + 5A extra tips it over.
I'll leave it to the experts to state what cable sq mm is required / desirable (as it will depend on install cable length and method).
The wire from the consumer unit to cooker switch going with the vernier I used is 4mm that’s the actual wire not the covering . Thanks for the replies I very much appreciate it
The wire from the consumer unit to cooker switch going with the vernier I used is 4mm that’s the actual wire not the covering . Thanks for the replies I very much appreciate it
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local