Wiring Electric Underfloor Heating

Discussion in 'Electrics UK' started by Kadi, 19 Feb 2018.

  1. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    14,042
    Thanks Received:
    1,220
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    There are models with remote sensors, however mine simply have two sensors one for air and one for water, the latter auto compensates the air temperature reading, and the radiators are modulated just like the boiler, so other than first turn on with a cold house, they are not that hot, unlike the old mark/space control, the modern system regulates the output so neither boiler or radiator valves switch on/off both gradually reduce output.

    The problem is although there are thermostats like EvoHome and Nest which use an industrial standard opentherm many boilers can only have the output modulated by either return water temperature or that manufacturers own modulating thermostat the latter may not be able to talk to electronic TRV heads. So in mothers house with a Bosch boiler if I used EvoHome it has to be set to use the mark/space ratio not modulate the boiler, it needs Bosch's own thermostat think it's call Wave to electrically modulate the boiler.
     
    • Like Like x 1
  2. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    18,482
    Thanks Received:
    1,835
    Location:
    Oxfordshire
    Country:
    United Kingdom
    I'll wave the pedantry flag here. ALL electric work is subject to Part P!

    Have a read here
    https://www.diynot.com/wiki/Electrics:part_p:Statutory-Instrument

    Maybe what you are thinking about is the requirement to notify the work if done in a bathroom?
     
  3. Seb101

    Seb101

    Joined:
    29 Jul 2015
    Messages:
    265
    Thanks Received:
    8
    Country:
    United Kingdom
    Pedantry accepted. Yes I was referring to the notification requirement.
     
  4. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,787
    Thanks Received:
    2,857
    Location:
    London
    Country:
    United Kingdom
    No.

    This is Part P:

    [​IMG]

    It is not pointless pedantry to point out that the requirements for doing work safely apply to everything, not just notifiable work.
     
  5. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,787
    Thanks Received:
    2,857
    Location:
    London
    Country:
    United Kingdom
    Maybe we should check that Kadi does not live in that land mass immediately to the left of most of England, approximately the size of Wales....
     
  6. Kadi

    Kadi

    Joined:
    19 Feb 2018
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom

    Hi Seb, firstly thank you for your advice related to my original question - it's much appreciated.

    Secondly i'll try and answer as best i can! My knowledge of the RCD/RCBO is limited although i seem to recall its 32Amps/30mA (if that helps?). I thought i had a picture which may have helped but i haven't... i'll take a look at it tonight. The current circuit has 1.3kW attached to it and its purely dedicated to the underfloor heating and all i wanted to know was if i could attach another 750w to the circuit from the junction box. If i can then i will go ahead and book in an electrician (even if i can carry out the work myself i wouldn't :/).

    A fused spur off the sockets would be more work as there aren't any located on the outer wall of the hallway - they're on the other side of the rooms.
     
  7. Seb101

    Seb101

    Joined:
    29 Jul 2015
    Messages:
    265
    Thanks Received:
    8
    Country:
    United Kingdom
    32A/30mA would almost certainly be an RCBO. If it is dedicated to the UFH (turn if off to check and see if anything else stops working) then you have plenty of spare capacity (32A x 240V = approx 7.5kW of capacity).

    You're good to go.
     
    • Thanks Thanks x 1
  8. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    14,042
    Thanks Received:
    1,220
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    Some UFH mats stipulate area allowed to be protected by one RCD, it would seem there is some leakage so exceeding the limit could result in it tripping with no fault, you need to read the paper work that came with the units, it varies make to make, you do have the power required. Because it is the earth leakage which limits, then will need a RCBO which is a RCD and MCB combined and it depends on the design of the consumer unit if it will take RCBO's and how many it can take.

    I still ask the same question, how is the central heating controlled? As adding UFH could mess up the central heating.
     
  9. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page