Wiring questions - installing new thermostat

Discussion in 'Plumbing and Central Heating' started by jespencer, 26 Dec 2012.

  1. jespencer

    jespencer

    Joined:
    26 Dec 2012
    Messages:
    8
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    New Thermostat Honeywell (Homeexpert) THR870C

    Old thermostat Drayton RTS-1

    I have three wires poking out out my wall, appears Honeywell is a two wire unit.

    Wires are blue, brown and yellow+green.

    http://www.homexpertbyhoneywell.com/Documents/EN Manuals/THR870CUK-EN-d05.pdf

    I have the Brown going into A, the yellow+green into C and the blue taped off. The thermostat is calling for heat but the boiler is not responding.

    Any helpers out there? Thanks.
     
  2. Sponsored Links
  3. doitall

    doitall

    Joined:
    8 Jan 2005
    Messages:
    19,003
    Thanks Received:
    1,538
    Location:
    Bath
    Country:
    United Kingdom
    The simple bit is the switching pair is A_B.

    But first you need to say where (No) the wires were connected in the old stat
     
  4. jespencer

    jespencer

    Joined:
    26 Dec 2012
    Messages:
    8
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    My friend took off the old baseplate before we took a picture, but I am reasonably confident that

    Blue - neutral

    Brown - live

    yellow green - ground...

    Does this make sense?
     
  5. doitall

    doitall

    Joined:
    8 Jan 2005
    Messages:
    19,003
    Thanks Received:
    1,538
    Location:
    Bath
    Country:
    United Kingdom
    There'll be a big bang if it isn't.

    Move the wire from C to B and keep the fingers crossed.
     
  6. mikely

    mikely

    Joined:
    11 Feb 2005
    Messages:
    305
    Thanks Received:
    72
    Location:
    Lancashire
    Country:
    United Kingdom
    No it doesn't, because the RTS1 requires Live, neutral and switched live. See http://www.draytoncontrols.co.uk/WorkArea/DownloadAsset.aspx?id=10497
     
  7. jespencer

    jespencer

    Joined:
    26 Dec 2012
    Messages:
    8
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    Have taken another look at the old rts one

    N - blue

    L - brown

    3 - "call" yellow / green.

    Assuming this is correct, for the new unit,


    A - Brown

    B - yellow + green?

    Thanks,
    J.
     
  8. doitall

    doitall

    Joined:
    8 Jan 2005
    Messages:
    19,003
    Thanks Received:
    1,538
    Location:
    Bath
    Country:
    United Kingdom
    Yes as I said move the yellow/green from C to B. :rolleyes:

    And stick the blue in N.
     
    • Thanks Thanks x 1
  9. RF Lighting

    RF Lighting

    Joined:
    31 Mar 2006
    Messages:
    19,627
    Thanks Received:
    1,297
    Location:
    Leeds
    Country:
    United Kingdom
    Sounds like you need an electrician to take a look at your wiring.

    green & yellow should NEVER be used for anything other than earth.

    Connecting an EARTH wire to a live terminal is going to end up with either a dead thermostat, or someone else who has the misfortune to work on this wiring being killed.
     
    • Thanks Thanks x 2
  10. Sponsored Links
  11. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    16,492
    Thanks Received:
    1,494
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    Although likely Brown to A and Blue to B one should not really guess. If wired correct as I would expect there should have been a brown sleeve on the blue wire.

    I have come across many odd systems which do not follow the rules including using a green/yellow as a line wire and this was original wiring on a Persimmon Homes house which one would have thought would have been wired correct.

    So really only option is call an electrician to sort it out.
     
  12. mfarrow

    mfarrow

    Joined:
    2 Nov 2009
    Messages:
    2,126
    Thanks Received:
    243
    Location:
    Warwickshire
    Country:
    United Kingdom
    Why? Just over sleeve the green/yellow with brown, assuming the thermostat isn't installed in a metal back box and doesn't need an earth in its own right.
     
  13. dingodeano

    dingodeano

    Joined:
    19 Sep 2007
    Messages:
    454
    Thanks Received:
    14
    Location:
    Staffordshire
    Country:
    United Kingdom
    Green and yellow should NEVER be used as a live conductor.
     
  14. RF Lighting

    RF Lighting

    Joined:
    31 Mar 2006
    Messages:
    19,627
    Thanks Received:
    1,297
    Location:
    Leeds
    Country:
    United Kingdom
    That's nothing but a dangerous bodge.

    You really need to stop giving out electrical advice if you have no idea of safe working practices, regulations or the law which governs this sort of work.
     
  15. doitall

    doitall

    Joined:
    8 Jan 2005
    Messages:
    19,003
    Thanks Received:
    1,538
    Location:
    Bath
    Country:
    United Kingdom
    The blue is a neutral Eric not a switch wire. :rolleyes:

    The OP has said where they were connected and the rest is simple.

    And I've seen 1000s that have been wired by so called sparkies that use the G/Y as a switch wire, not sleeved.
     
  16. doitall

    doitall

    Joined:
    8 Jan 2005
    Messages:
    19,003
    Thanks Received:
    1,538
    Location:
    Bath
    Country:
    United Kingdom
    If the sparky knew his job he would test before he sticks his fingers in and starts playing.

    In an ideal world you are right they wouldn't use the earth wire, but there's as many that do as don't.

    If it's sleeved or taped red I don't see the problem, and in any case if you know what you are doing you will be able to relate to the numbers the wires are connected too.
     
  17. RF Lighting

    RF Lighting

    Joined:
    31 Mar 2006
    Messages:
    19,627
    Thanks Received:
    1,297
    Location:
    Leeds
    Country:
    United Kingdom
    You can't try and pass the buck like that. If you knew how to drive you wouldn't need a seatbelt or airbag in your car. What a ridiculous statement to make.

    The fact that you don't see the problem just shows you shouldn't be advising anything to do with electrical work.

    It's not about ideal world conditions it is the most basic of electrical safety principals.
     