I\\\'ve installed down lights (5x50 watt) on .5mm2 cable is this too lite should I use a heavier gauge cable?
 
proberly will be alright but........

if i found that in my house i would definately change it! :shock:

i take it its not done in singles?
 
250W / 12V = 21 amps

Rating of 0.5 sq mm flex is 3 amps (Table 4H3A in BS 7671).

I'd say 'you do the maths' but I already did it for you.
 
dingbat said:
250W / 12V = 21 amps

Rating of 0.5 sq mm flex is 3 amps (Table 4H3A in BS 7671).

I'd say 'you do the maths' but I already did it for you.


Thanks for your reply, so quick on new years eve, I'm using 240V instead of 12V, can you respond again, I kind of think the wire is too light for 240V
 
mst said:
proberly will be alright but........

if i found that in my house i would definately change it! :shock:

i take it its not done in singles?

Thanks for the reply, its not single cable, two core, but I think I may rewire soon. At the moment the lights only go on for five minutes at a time but could be a problem in the future if on for any length.
 
You have a 250W load on a 230V supply, so the current draw, when all the lamps are lit, is 250 divided by 230, which is slightly over 1 Amp. Your cable is rated at 3 Amps. Its safe.
 
kevnurse said:
You have a 250W load on a 230V supply, so the current draw, when all the lamps are lit, is 250 divided by 230, which is slightly over 1 Amp. Your cable is rated at 3 Amps. Its safe.

Thxs
 
Sorry about that, for some reason when I read your post I automatically inserted the words 'extra low voltage' somewhere in my head.

There are so many non-compliant issues with the use of downlighters that I always fear the worst!
 
dingbat said:
Sorry about that, for some reason when I read your post I automatically inserted the words 'extra low voltage' somewhere in my head.

There are so many non-compliant issues with the use of downlighters that I always fear the worst!


Thanks for the help anyway, its great to get help and I likewise always fear the worst. The lights have been in operation for six months now without problem but I knew there was this question in my mind that I needed answered. Happy new year.
 
orc said:
The lights have been in operation for six months now without problem but I knew there was this question in my mind that I needed answered.

There are probably a number of issues you are unaware of, not least the method of termination of conductors and enclosure thereof. That there are not more problems with electrical installations generally is more a matter of sheer luck than of good practice.

Practically anybody can connect electrical equipment so that it works; it's when it fails that the real problems can occur. I see very few DIY installs that fill me with any confidence (I see quite a few so-called professional jobs that make me shudder, too.)
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top