Thanks for the reply, its not single cable, two core, but I think I may rewire soon. At the moment the lights only go on for five minutes at a time but could be a problem in the future if on for any length.
You have a 250W load on a 230V supply, so the current draw, when all the lamps are lit, is 250 divided by 230, which is slightly over 1 Amp. Your cable is rated at 3 Amps. Its safe.
You have a 250W load on a 230V supply, so the current draw, when all the lamps are lit, is 250 divided by 230, which is slightly over 1 Amp. Your cable is rated at 3 Amps. Its safe.
Thanks for the help anyway, its great to get help and I likewise always fear the worst. The lights have been in operation for six months now without problem but I knew there was this question in my mind that I needed answered. Happy new year.
There are probably a number of issues you are unaware of, not least the method of termination of conductors and enclosure thereof. That there are not more problems with electrical installations generally is more a matter of sheer luck than of good practice.
Practically anybody can connect electrical equipment so that it works; it's when it fails that the real problems can occur. I see very few DIY installs that fill me with any confidence (I see quite a few so-called professional jobs that make me shudder, too.)