Can anyone help i have been having problems with this boiler running for a day then locking out, it has a new burner on and the combustion is stop on, all baffles are correct and flue is not blocked , it is a oil boiler, there is plenty of oil and oil line is clear. haS anyone got any suggestions would be crateful thanks. :mrgreen:
 
Sponsored Links
Is the tank higher than the burner, or is the pump having to draw the fuel? Is there a filter that has not been bled properly? Are you sure there is no fuel contamination?
 
Sponsored Links
Why was the whole Burner replaced - seems a bit extreme!! if the old burner displayed the same symptoms then the fault is SITE RELATED and as said fuel starvation blocked oil filter, blocked/faulty fire valve if on a tigerloop or 2 pipe system ,air ingress into fuel line ;)
 
Is the tank higher than the burner, or is the pump having to draw the fuel? Is there a filter that has not been bled properly? Are you sure there is no fuel contamination?
Thanks for the reply, the tank is higher than the boiler, there is a cabnet htr about two meters away from boiler and has no problems , oil line is clear and filter is clean , its a bit baffling dont u think
 
We had trouble with our Heatslave earlier this year, the oil tank was topped up the delivery driver forgot to put the lid on the filler cap, didnt notice it, some rain got in and settled to the bottom, it kept locking out intermittently, drained off about a gallon water/oil has worked fine since.
 
Boss, doesn't your outlet come from the side rather above the bottom to allow for sludge and water?

Or have you tipped it up to get the last ( dirty ) dreggs out when you have forgotten to re order in time?
 
Boss, doesn't your outlet come from the side rather above the bottom to allow for sludge and water?

Or have you tipped it up to get the last ( dirty ) dreggs out when you have forgotten to re order in time?

Tony,
It's a long time since you saw an oil tank.
Plastic ones have to be installed horizontal and only have one outlet.
 
there is no problem with oil line as i can see because there is a cabnet htr about two meters away and has had no pronlems[/quote]

Is it possible the cabinrt heater is starving the heatslave of fuel?
 
We had trouble with our Heatslave earlier this year, the oil tank was topped up the delivery driver forgot to put the lid on the filler cap, didnt notice it, some rain got in and settled to the bottom, it kept locking out intermittently, drained off about a gallon water/oil has worked fine since.
all sorted the tits
knocked the valve shut no oil going to boiler , job is about three hours away didnt fancy going back ,cheers
 