would you trust a 10amp MCB on a 3a central Heating Circuit

Discussion in 'Electrics UK' started by andyr123, 21 Mar 2017.

  1. andyr123

    andyr123

    Joined:
    17 Oct 2005
    Messages:
    113
    Thanks Received:
    0
    Country:
    Ireland
    Moved into this new house in Dec 2016 , house was built in 2008 - and I notice that although every heating controls (time clock, zone valves, boiler, pump) says protect with DP switch fitted with 3a fuse that the only thing that is protecting the circuit is a SP 10a MCB in the consumer unit. There is no DP spur anywhere with a 3a fuse fitted in it either next to the time clock or airing cupboard , in boiler house, in fact nowhere else. Can I trust if there is an electrical fault for the 10a MCB to trip?

    Tough one this, didnt know whether to post in the Electrics or Plumbing and Heating forum, but i thought I would post in this forum in the end.
     
  2. Sponsored Links
  3. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,778
    Thanks Received:
    4,246
    Location:
    Retired to:
    Country:
    Portugal
    Fuses are to protect the circuit wiring; not the accessories - so, providing the wiring has a current carrying capacity of 10A or more then all is well. Although this can be ignored if the system cannot overload a lesser cable.

    The standard 'requirement' for a DP switch with 3A fuse is just that - it's just what they write.

    A DP switch to isolate the whole heating system is standard practice and a good idea and it is easiest to fit a Fused Connection Unit (the circuit is the 'spur') and fit a 3A fuse as the system will not require more than that.



    Look at it another way - what do they do in places where FCUs and fuses do not exist and the circuit will be 16A?
     
    • Thanks Thanks x 1
  4. andyr123

    andyr123

    Joined:
    17 Oct 2005
    Messages:
    113
    Thanks Received:
    0
    Country:
    Ireland
    thanks for the reply - so the short answer is? :)
     
  5. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    75,020
    Thanks Received:
    4,349
    Location:
    Crossgates, Europe
    Country:
    Cook Islands
    As you are in a country which uses the wonderful BS1362 system, fit a DP switched FCU and put a 3A fuse in it. It will be red.

    If you want, you can put a label on it saying "Boiler - 3A fuse"

    A labelmaker or just a marker pen will do.
     
    • Thanks Thanks x 1
  6. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    Or you could find out if the equipment you have is sold in other parts of the world, and if it is ask the company why they don't supply the UK market with products which are as safe and well made as the ones they supply elsewhere. Tell them you are minded to make a complaint to Trading Standards about the supply of dangerous electrical items.
     
    • Thanks Thanks x 1
  7. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    18,890
    Thanks Received:
    1,775
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    For a portable appliance any fuse required which is less than 16A has to be included in the appliance the fuse in the plug or FCU only protects the cable, however a central heating boiler is not really potable so the manufacturer can stipulate if an external fuse is required, having said that every one I have worked on does have a fuse inside the boiler so unlikely the boiler needs an external fuse, as to double pole switching it is always good when you have RCD protection and 2008 was the year when RCD protection for all circuits came in, to have a double pole isolator so if something should go wrong with the boiler then you can isolate it and so continue using other equipment supplied from the same RCD.

    So although unlikely to cause a problem, if you want to cure it there are three options open to you, the 13A plug, the FCU or a double pole RCBO you can't get double pole MCB's single module width, but you can get RCBO which although the overload does not monitor the neutral the neutral is switched. Personally I would not worry about it.
     
    • Thanks Thanks x 1
  8. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    8,949
    Thanks Received:
    1,128
    Location:
    Dorset
    Country:
    United Kingdom
    Short answer - make sure a 3 amp fuse protects the boiler.

    Most boilers do stress how important this is to protect the circuit board in the boiler. Replacing that could prove expensive.

    A switched fused spur with a 3 amp fuse is the norm for protecting a boiler.
     
    • Thanks Thanks x 1
  9. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,778
    Thanks Received:
    4,246
    Location:
    Retired to:
    Country:
    Portugal
    As Eric says, boilers have fuses in them.

    A 3A fuse would not be much good for the circuit board.
     
  10. Sponsored Links
  11. Risteard

    Risteard

    Joined:
    18 Jun 2010
    Messages:
    2,189
    Thanks Received:
    159
    Location:
    Derry, Ireland
    Country:
    Ireland
    This poster is in County Sligo in the south of Ireland - he is not in the UK and electrical work is NOT carried out to BS7671. He also is prohibited from carrying out Restricted Electrical Works under pain of prosecution and imprisonment.
     
  12. 333rocky333

    333rocky333

    Joined:
    12 Jan 2008
    Messages:
    8,457
    Thanks Received:
    911
    Location:
    Essex
    Country:
    United Kingdom
    May be worth asking the plumbers, maybe theres a gas reg requiring DP switching for the boiler, when there working on gas you dont really want a spark from N toE
     
  13. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    75,020
    Thanks Received:
    4,349
    Location:
    Crossgates, Europe
    Country:
    Cook Islands
    Look at the MIs.
     
  14. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    Indeed.

    1) Sorry for forgetting/not noticing his location. Strange that you should know the difference, however....

    2) Please tell us how likely it is that a DIYer would face prosecution, let alone imprisonment.

    3) If FCUs are not allowed in RoI, then how can he provide the fusing? If they are used, then everything I said about asking the manufacturer why they are supplying goods which are not as safe as the ones they provide in mainland Europe still applies.
     
  15. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    Would they know about the regulations in other countries?
     
  16. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    7,308
    Thanks Received:
    565
    Location:
    London
    Country:
    United Kingdom
    But they are guidance only. You don't have to follow them, especially if they are wrong. And they are wrong as has already been pointed out the boiler should have its own internal fuse, an external one is to protect the wiring only.
     
  17. andyr123

    andyr123

    Joined:
    17 Oct 2005
    Messages:
    113
    Thanks Received:
    0
    Country:
    Ireland
    What is MIs sorry?
     