200 ohms is the max for reliability in guidance docs.
The max in the regs 1666 ohms for a 30mA RCD protected socket circuit (50v/0.03A=1666 ohms).
So although the theoretical maximum is above 200 ohms, this should not be exceeded as it is considered unreliable.
Ok so to get a proper correct figure disconnect the bonding to the water and gas (as pictured)?
I think I may get the service provider to see if they can PME the earth but obviously the Ze needs to be below 0.35 for them to do this, if so is the main rcd ok to remain?
What have you been doing since then? Did you do the T&I course? Did you pass the exam? Or given that you can't even do simple cable sizing calculations or basic maths, was it all too much for you?