Moving Cooker Switch
22 Nov 2010
I need to move my cooker switch by about 1 foot in order to create space to fit a cooker hood.
The existing switch cabling is buried into the wall and is protected by steel tube ducting.
My question is: Can I use armoured cabling (10mm thick which will be buried into the wall of course) for the 1 foot extension and just connect it to the existing cabling/steel ducting?
Cheers
How are you intending to connect the armoured cable to the steel conduit and the existing wires?
I was planning on feeding the armoured cable into the existing armoured ducting as far back as the nearest steel junction box. Then either solder the live and neutrals together or use a terminal connector. The earth on the armoured cable would also be connected to the earth terminal within the steel junction box.
Would that be a safe idea?
Is the existing tube metric 20 mm circular conduit? Or is it the older imperial conduit? Or is it oval?
How many wires inside tube?
Soldering is a bit of a no-no as far as ive been aware.
However I understand it is considered that where needed its acceptable to join a wire with terminal block and plaster over smooth. Not ideal, expcially where the run is then not straight or directly above/below the fitting but proberbly they best option here. I would just use the equiv sized Twin+Earth rather than SWA.
Daniel
No its not.
Joining cables in a wall, or soldering?
I presume the former, and if you can get the cable up the conduit as far as the ceiling void then so much the better, but if have seen registered professionals do worse...
Daniel
You can not bury joints like that in the walls, it does not conform to BS7671 as a secure and safe method.
The best method here would be to completely replace that run of cable and route it in a permitted safe zone. I doubt 10mm SWA is going to feed through the metal conduit they have in place.
Not sure you can get SWA that small - what would it be - 1mm² 2-core? Not suitable for a cooker circuit, that's for sure.
You've never actually worked with armoured cable, have you. There's no way you could do what you describe with the armour.
http://www.diynot.com/wiki/electrics:swa-gland
By the sounds of it you should either re-route the entire cable, or get an electrician to run a short length of conduit from the old switch box to the new location.
[EDIT]Broken links fixed[/EDIT]
BAS on the group of 4 links only the first works.
Noticed this before, just to let you know.
Thanks for that. IET links fixed. IMO website organisers who break links should have their willies cut off and buried below low-tide line.
The Wayback archive link works for me....
Try clicking the "Impatient?" button.