One Ring Failing - Anything I can check?
Well it looks like I may have been running on a ring with a loose connection for a while. And a 2nd fault has caused a complete break in the ring. The electrician was able to locate the section and I remembered a screw down junction box under the floor (near the CU). So floor up, screw tightened and problem solved. I found another 2 junction boxes in the same floor space - 1 which needed tightening (hopefully the 1st fault). Electrician coming back to take some reading on the ring. Thanks
Great.!
That proves the requirement for junction boxes to be accessible!
As you have found out, quite often, the JB has been hidden under the floor for a decade or two (or buried in the wall :evil: ) and nobody knows it is there.
So I see.
What's the story with that armoured cable above the JB? I can see the steel armour, I hope there aren't bare conductors coming out of the end :?: :?
That's an old armored cable (replaced when extension went in)
Electrician came back to test, still had a neutral fault between last socket and CU. He worked out which wire it was on. Wire disconnected, now converted to a radial and downgraded MCB from 32 to 20.
He said that was best.
Best option if you don't want the hassle of replacing the damaged leg. Not necessarily the BEST solution but not the worst.
Do you only have one radial circuit then? Would indicate the break was on a leg from the cu to the first/last point and may not be that hard to fix
Oh may bad. Didn't read that post very well at all.
Shame it wasn't a mid ring break. Sometimes two radials are better that one ring final
Oh may bad. Didn't read that post very well at all. Shame it wasn't a mid ring break. Sometimes two radials are better that one ring final
People say that, but I don't really understand what the perceived advantage is meant to be. If we were talking about 32A radials, that would be different, but a 20A sockets circuit seems a bit iffy to me, in as much as it theoretically can only support about 1½ 13A loads.
my mistake it was a 16 amp MCB
That's worse (in terms of power availability). It ought to be able to be at least 20A (possibly 25A if one is available for your CU). Regulations require that the current-carrying capacity of cable used in a ring must be at least 20A, so a 20A MCB ought to be fine.
It is for 7 sockets in a living room and study - with nothing that draws much. He said even if I needed to I could run a couple of Electric heaters.
It's not a ring.
It was a ring, until the electrician disconnected the cable between the last socket and the CU, turning it into a single radial. As I said, if it used to be a reg-compliant ring, the CCC of the cable would have to have been at least 20A, so the newly created radial should be able to have at least a 20A MCB, if not (depending on cable installation method and MCB availability) a 25A one.