what code for flex used to wire 15amp radial on EICR?, got a CU change to do later in the year and found a radial wired in flex
1.5, on 15A 3036 at the moment, only running a fridge, don't like to condemn something just because it's unconventional
Nothing wrong in using flex.
413.3.4 Flexible cables and cords shall be visible throughout any part of their length liable to mechanical damage.
521.9.3 A flexible cable or flexible cord shall be used for fixed wiring only where the relevant provisions of the Regulations are met.
I have seen people try and use that to say they should not be used, however if one looks at caravans then.
721.521.2 The wiring systems shall be installed using one or more of the following:
(i) Insulated single-core cables. with flexible class 5 conductors, in non-metallic conduit
(ii) Insulated single-core cables, with stranded class 2 conductors (minimum of 7 strands), in non-metallic conduit
(iii) Sheathed flexible cables.
All cables shall, as a minimum, meet the requirements of BS EN 60332-1-2.
Non-metallic conduits shall comply with BS EN 61386-21.
Cable management systems shall comply with BS EN 61386.
In this case it is concealed in a wall and really one has to use some common sense. When we are using a flexible cable to the rating given for flexible cable then it needs to visible but where it is down graded to allow for being buried then there is no reason why it needs to be visible rate a 70°C flex to same as a 70°C flat twin and earth and OK. With a 60°C flex allowance must be made for the lower temperature rating. However there is no reason why it should not be used.
1.5mm² is too small or the 15A fuse is too big - unless consideration has been taken to permit the omission of overload protection.
As it is only supplying a fridge, a 10A fuse could/should have been used.
Thanks folks, I'd been thinking along the lines of dropping it to 16A (60898, B) when I do the board swap, couldn't think of any real reason to condemn it and suggest rewiring, as to whether my customer knows if I'm asking on a DIY forum, my exact words to him were, "I think it should be ok to swap onto the new board, but I'll check before commiting myself to that as it's not something I've come accross before" which strictly speaking isn't true, last time I came accross something like this the test results were rubbish so I condemned it on different grounds.
Yes this is supposedly a DIY forum (albeit with a section for gas engineers), but I also happen to know from past experience that people like securespark, ericmark, EFLImpudence etc often frequent this page and invariably offer sound advice to those mortals who like to check their own judgement at times, and as someone who doesn't have the arrogence to believe he knows everything, I don't mind asking occasionally, I have on many occasions given advice and taken part in discussions where other people have sought reassurance, and tried to do that without passing judgement, obviously a skill which many manage to display, but sadly not all
One way round is to feed the flex from a 13amp fuse connection unit with flex outlet.
I know of a large, multinational corporation, that in the UK, uses YY almost exclusively for their fixed wiring.
If it doesn't need to H07 or SWA, it's YY.
Get on many major new construction projects and you'll find the lighting wired throughout using flex 7.
Everything on the LV side is wired in flex using plug in factory made terminations.
There is a big difference between not knowing everything and not knowing something so basic and so easy to find in the Wiring Regulations that it makes you a charlatan to be taking money from people to provide professional expertise.
most Tesco express stores are the same, even using 5 core 6mm YY on 3 phase circuits