The current Hager busbar is almost (if not completely) identical to the slightly older range. Hager themselves have confirmed backwards compatibility of all of the new range, with all of the old range. Indeed - if the guy fits an RCBO it's going to be from the current range I would suspect.the engineer would have to source a bus bar, that consumer unit is an old range, although possibly ok, it may not be compatible to take a current range busbar
All of the options are safe. They may work differently and have implications when things go wrong.I guess we just want what is safe and cost effective.
Of course it could, as long as the consequences of RCD operation are considered.That could be done, but would put all of the sockets in the property on a single RCD, and could in no way be considered to comply with section 314.
Really?Ban all sheds option could become more time consuming. IF the bus bar has been cut, the engineer would have to source a bus bar, that consumer unit is an old range, although possibly ok, it may not be compatible to take a current range busbar.
It's perfectly do-able.I would not particularly want (and do not have) an RCD on the kitchen circuit but that is not now allowed when new work is done.
Untrue. Read 411.3.3 Exception (b).All socket outlets must have an RCD
A value judgement which should be the topic of a discussion with the customer. I'll bet there are still loads of flats being built with just 1 RCD in the CU. And I wasn't suggesting putting the whole house on the same RCD.Option 3 (which the electrician did not quote for) is to move the circuit breaker for the kitchen sockets onto the RCD side of the consumer unit. This achieves the same result as option 2, but with the added disadvantage that any fault on any socket in the house results in the entire lot having no power. This can also occur with a large number of appliances plugged in, as many have a tiny amount of leakage to earth as part of their design. With the entire house on a single RCD, such problems are far more likely.
This does not comply either because of :
314.1 Every installation shall be divided into circuits as necessary to:
i. avoid danger and minimize inconvenience in the event of a fault
How many kitchen appliances do that?....
iv. reduce the possibility of unwanted tripping of RCDs due to excessive protective conductor currents not due to a fault
I disagree. It could be.Option 3 is not compliant.
I just think the blanket demand for RCDs is OTT and unwarranted.OOI -why do you not particularly want an RCD on the kitchen circuit?
What criteria do you think should be used to determine if an RCD should be installed?I just think the blanket demand for RCDs is OTT and unwarranted.
The OP's case being a good example of this.
Therefore, there should, IMO, be a case of more appropriate determination whether an RCD should be fitted.
What voltage would you be happy to see exposed conductive parts reach because of slightly worn elements?As for my kitchen, I just don't want any tripping because of slightly worn elements or similar things.
Whatever one thinks about RCDs, it is seemingly a bit odd to require RCD protection of just one (new) socket on a circuit, whilst all the others on the same circuit remain without such protection.I just think the blanket demand for RCDs is OTT and unwarranted. The OP's case being a good example of this.
With a typical earth component of the EFLI, the current required to raise the voltage of exposed-c-ps to a worrying level would normally be umpteen times the In of the circuit's OPD wouldn't it?What voltage would you be happy to see exposed conductive parts reach because of slightly worn elements?
That's how changes in practices happen...Whatever one thinks about RCDs, it is seemingly a bit odd to require RCD protection of just one (new) socket on a circuit, whilst all the others on the same circuit remain without such protection.
It usually is, but there is no reason why there can't be 'transitional provisions' - e.g. in this case only to require RCD protection of new sockets on an existing circuit if the result would be that the proportion of RCD-protected sockets on the circuits exceeded some specified level, or something like that.That's how changes in practices happen...