Adding a lighting spur to socket spur
21 Dec 2022
Hi there
I am hoping to confirm my plan for adding a lighting spur to a socket spur for a TV socket and some LED downlights.
Currently I have a socket on an existing ring. From this I plan to wire to:
FCU with 13 Amp fuse >>>> Double socket >>> FCU with 3 Amp fuse >>> Lighting ring
Will be using 2.5mm2 T+E cable up to the FCU with 3 Amp fuse and after this will use 1mm2 cable for the lighting ring.
Please let me know if any comments or concerns with this suggested set up?
Many thanks
Ben
Hi there
Many thanks
Ben
The lighting circuit is not likely to require a ring
Definitely not you mean, but I think you know he didn't mean that....maybe
I don't know what he means;
Some use the term 'ring' as a global replacement for 'circuit'.
Some assume all circuits are wired as rings
Thanks all - very helpful.
Yes, apologies don't mean a lighting ring - meant a "circuit".
That would be fine.
In fact, you don't really need 2.5mm² cable for any of it - 1.5mm², or probably even 1mm², would do with common installation methods (buried in a wall etc.).
I don't think many would argue about using smaller cable downstream of the first FCU (with 13A fuse) but those unable to think for themselves might be less happy with cable smaller than 2.5mm² between ring and that FCU, but seemingly only becasue that does not appear as an example in the guidance given in an Appendix of the Wiring Regs!
LOL! anyway you can wire lights as a ring if you want, not many do though but I do know of one who used to back in the 70s
Actually I just remember - I do know another, years back I was doing an inspection and correcting some lighting. I discovered two separate lighting circuits joined together near the radial ends. could have been rather interesting to see if one MCB knocked off for servicing the other one still supplied the whole lot. Not to mention the possible horror of trip times on overload/shorth/earth fault (although it did actually have an RCD so earth fault not really an issue) but obviously I couldn`t leave without sufficient investigation and correction to render safe, it was a bit of a dogs breakfast to trace out in order to improve things.
Two breakers on different legs of one ring final often with the same two breakers on different legs of another ring final was something I`d seen a few times though