Help with new heating and hot water system!
19 Nov 2014
London
Hi all, I appreciate you help in advance, and hope this post also helps someone else in the future!
I need to make a decision on what heating and hot water system to get installed. All new pipes are being laid, and I will have radiators everywhere (no UFH). My options after quite a bit of research:
  • System boiler: Vaillant ecoTec Plus 630 (30kW) Viessmann Vitodens 100-W B1HF (32kW), Worcester Greenstar 8000+ (30kW).
  • Unvented cylinder: Vaillant UniSTOR 250l, Joule Cyclone Platinum 250l (big price difference).
  • Controller / thermostat: Drayton, Honeywell, Tado X, or the control / thermostat from the brand of the boiler.
The other question is of course the setup - I was thinking two zones + TRVs, or if that would be too complex, TRVs or zones (in that priority order - as I feel as though room control would be better?).
The trouble I am having is to match everything together in a way that the system runs most efficiently. I like the idea of modulation - but this has led me down a bit of a rabbit hole - my understanding:
  • Viessman works with Opentherm, but may be expensive / difficult to get parts? With Opentherm, it could modulate with Drayton, Honeywell, Tado X which all have smart TRVs. Tado was my preference, but with the recent subscription scandal I think I'd like to go for one of the others which I am less familiar with.
  • Vaillant is eBUS - can't modulate with Drayton, Honeywell, but can with an EU version of Tado v3+ if I want TRVs. I'd rather go with the Tado X + see my comments above. The other option is Vaillant's own controls but they are v. pricey, and their TRVs are discontinued.
  • Worcester 8000+ - it's the loudest, has an aluminium heat exchanger (sub-standard to the stainless steel ones in the options above?) and uses it's own modulation protocol, so only their own controls would do the trick. They do have TRVs but I struggled to find much info / reviews on them.
  • I have also read about Ideal and Baxi boilers but reviews seem to be rather mixed...
Thank you!
Modulation, is simply the boiler being able to reduce it's output, at those times when it's full output is not needed. It works best, with intelligent control systems, which are able to tell the boiler to modulate down, and provides increased efficiency.
You don't have to buy Vaillant TRV's, the Vaillant control system works with any TRV's. I bought a full set of Vailant controls, for around £150, on ebay. Wireless display/ control, receiver for the boiler, the gubbins, for the airing cupboard, and the wireless outdoor sensor. It works a treat, much better than the on/off controls which I had, when the new boiler went it.
What does your GSR suggest?
We refurbished our house in 2013 and have 1 zone - big mistake. Definitely have 2 zones
Controls are simple. If you go for a Vaillant boiler stick with Vaillant controls etc.
How many rads are you going to have? If the system is set up as all modern systems should be with hot water priority then it’s very unlikely you need a 30kW boiler which will affect the minimum modulation.
If it’s a complete new system a full heat loss survey should be carried out and the system should be sized to work at a max flow temperature of 55 degrees.
You won’t get the most efficient system unless it’s properly designed
I question having an unvented cylinder which needs an annual test. I would prefer a system where I can decide when it is serviced and tested.
As to boiler make, not a clue.
As to the controls, I made mistakes, and had to modify the control method.
Ideal is all radiators on internal walls, each with a linked TRV head, connected to a hub which will with an analogue method control the boiler's output, like using Drayton Wiser TRV heads, hub, and OpenTherm to control the boiler.
But once one deviates from the ideal, one has to look at near enough engineering. So with a radiator under the window, we could put a wall thermostat on the opposite wall so not over cooled by the cold wall, but since the problem only exists until the thermals in the room are established, it may be better to still use the TRV head to trigger the boiler.
Much depends on how well insulated the wall is.
Also, where two or more rooms need about the same amount of heat, one could reduce costs, and only use a linked TRV head in one of those rooms.
It is a lot easier to alter control but adding more electronic TRV heads, to altering the plumbing from a master zone valve, and there is no point having a zone valve supplying a zone valve, so I favour the idea of using TRV heads to do all the control. It is far more flexible. So my wife's craft room even when up-stairs can be programmed to be heated during the day. And when we are not using the dinning room, it can be turned off, so saving money. It also allows a sequence so kitchen, then dinning, then living room are heated, and can stop heating dinning room earlier than living room for example.
Do you actually need a 30kW boiler? Have you had a heat loss calculation carried out?
Building Regulations require that new systems are designed to a maximum 55°C flow temperature so ensure you get an installer who is up to date and knows how to do this. It means radiators will be slightly larger.
The Vokera Pinnacle system boiler is well worth a look. From the same stable as Viessmann, and I know a few Viessmann guys who have switched to fitting Vokera instead. 11:1 modulation, stainless steel single coil heat exchanger, OpenTherm, and a 12 year warranty.
As @Razor900 and @muggles
Get the same controls and cylinder as the boiler.
They will all be under the same warranty and will work more efficiently together.
System has to be designed for low temp circulating fluid as per building regs.
Servicing a UV is a 10 minute job done same time as boiler service. If you have it done - most people don't.
As said above a 30kw system boiler is way over sized for the majority of homes. What is the heat loss of the property, that is what determines the size of boiler.
As also already said if you go with Vaillant or Worcester then use their controls. You can use standard TRV’s or so called smart TRV’s but IME standard TRV’s are better for the efficiency of most homes, it depends on your specific home and requirements.
Another thought…… don’t install an S plan, have a PDHW system with a diverter valve.
In the case of my system, the original installation, back in the 80's, was designed to cope with drafty single glazed windows, and doors, which it coped well with. Since then, I added dg, cavity insulation, and new doors, massively reducing the heat loss. That, made my existing pipes and radiators bigger than needed, so they could achieve the same heating effect, at much lower, more efficient, boiler condensing temperatures.
An heating system designer is now legally required to do a proper heat-loss assessment, before installing a boiler, or an heating system, problem is, many do not, or don't know how. You should insist on this being done, and ask to see the details of the assessment to be sure. You can even do this, yourself, as a back-up. Our original boiler, was a 28Kw, none condensing, none modulating, cast-iron heat exchanger, with a permanent pilot light. Our new one, is an 18Kw Vaillant, 418, which copes perfectly.
Agreed, it does seem massive.
This I am not so sure about, maybe you can explain?
I suppose the eQ-3 61dmtMm13BL.jpg is not really a smart TRV, the Wiser
is, as it is claimed to work out how long it takes to heat the room and switch on before the time set, so the room is warm at the time set, and I see a problem with the Wiser if the radiator is on an outside wall, as it could turn the boiler on prematurely.
However, the these
seem daft. How can anyone set the room temperature when they start to open 2°C to 3°C from point where fully open?
It is down to the setting of the lock shield valve, if with
these the lock shield valves were left wide open, the home would heat a room at a time, all water will go through the easiest radiator until the TRV starts to close, and then it will go through the next easiest radiator, as long as boiler not turned off, it will in the end heat whole house, and maintain each room at the temperature set by the TRV, but turn the heating off, with for example a time clock or wall thermostat, and the process starts all over again when switched back on.
Also, the TRV takes time to move, this one 61dmtMm13BL.jpg exercises at midday every Saturday to stop the pins sticking, it takes around 4 minutes to fully open, then fully close, and if hot water hits a radiator for 2 minutes without some restriction the radiator will get stinking hot, this will initiate a hysteresis, as the room will overheat, so we need to slow down how fast the radiator can heat up.
The method is to use a differential thermometer on the input and output pipes, I do actually have one, but most people don't, so we look for another method to set the lock shield valve.
A good start point is to close the valve fully, then open ¼ turn at a time until one feeds one pipe get hot, and stop at this point, but that is only approximate, next we look at the TRV report, 4 TRVs-1.jpgclearly unless alternative heating, the current should not exceed the target, if it does, then the lock shield valve needs closing a tad. (Note the eQ-3 does not display current, my Energenie shown, Kasa and Wiser all show current and target, which means you can set the lock shield valve spot on. And with a modulating boiler rooms will be controlled within 0.5°C of the setting, however, I will admit, the Energenie has an OTT anti-hysteresis software, and I found to set at 20°C at 7 am, at 11 am it still had not heated to room to that point, so would set at 22°C at 7 am and 20°C at 8 am and that worked fine.
This does however mean that geo-fencing does not work, the Energenie head uses IFTTT so can be set to use geo-fencing, but to date not found any device which works with geo-fencing, it will turn heating off when you leave OK, but will not turn it back on again in time.
But the *123456 on a mechanical TRV head is useless unless the lock shield is already set spot on, when I removed the Energenie heads and replaced with mechanical before selling late mother's house, they worked A1, now the lock shield was already set, so you could move an electronic TRV head from radiator to radiator to set the lock shield valve. But the electronic head also allows you to program when a room is heated. In my house with 13 heated areas, if I heated them all 24/7 it would cost a fortune, so 4 rooms are on a motorised valve, (the flat under main house) and the remaining areas all have programmable TRV heads of which 9 are not linked, and one only is linked to hub and can fire the boiler. Main house also two wall thermostats can fire the boiler, and flat a bi-metal thermostat as flat, not used much in winter.
So I have 5 x eQ-3 TRV heads, 3 x Energenie TRV heads, 1 x Kasa TRV head, and 1 x Wiser head, 4 x mechanical TRV heads, a Nest Gen 3 wall thermostat in hall, a Wiser wall thermostat in living room, and as said bi-metal in the flat. Yes a mixture, I made mistakes, I was told the Nest would work with Energenie, that is not the case, I thought there was a linked wall thermostat which would work with Kasa, but found there was only a hard wired version, so fitted Wiser where it has an indepentent hub and wall thermostat wireless linked, in fact can program in up to 9 thermostats to work with the hub.
Interesting idea, I find the DHW does not use that much energy from the central heating boiler, as it has not cooled down enough between boiler, solar, or off-peak heating. I suppose the PDHW is what we called the W plan, similar to Y plan, but no centre position for the valve?
It enables you to have two different flow temperatures. A high temp for reheating the hot water and a super efficient lower temp for space heating.
Yes the valve acts as a diverter there is no mid position (y)
My system was originally installed as, and remains as a Y-plan, using a mid-position capable valve. That was the case, until I installed my Vaillant boiler, which used separate flow temperatures, for central heating, versus when it heats the boiler, which logically means, it can only now serve one need, at one time.
When boiler was swapped out, I took the opportunity, to replace the unreliable spring return valve and actuator, with a MOMO actuator valve, which has proven itself to be 100% reliable so far, but the MOMO still supported the mid-position. The actuator, connects to my fancy intelligent, Vaillant replacement, for the usual joint box in the airing cupboard. The Vaillant system, just ignores using the mid-position.
In use, because the central heating goes off, with any demand to top-up the hot-water cylinder temperature, you have to think about the timings a little. Set the HW heating to come on when there is less likelihood of need for CH, or set the CH with time to heat the house up first, then let it tackle the HW later.
Most people with that set up just leave the DHW on 24/7. A modern cylinder with a big enough coil to run PDHW usually has a heat loss low enough that it doesn't matter