Bypass valve
The boiler casing would need removing I would think to check for a 3 way valve.
I have a feeling that some mix (or cock) up may occured in the configuring of your boiler and that the displayed flow temperature could or might be taken off a probe attached to the HEX or something like that, but what is really depressing is that any engineer or whatever they call themselves would say that its normal to have this huge difference in temperatures despite confirming it with his own gear.
Then I’m right to feel like I was being palmed off. He was adamant the boiler was all perfect. But then ofcourse he would. It’s still under warranty for 6 years more.
I too suspect there’s a cockup. Are the diverters easy to remove If there is one there?
Let WB worry about the (if) 3 way valve.
Write down or take a snapshot of these (especially temperature values).
Had a look on the inside, do you see anything resembling a 3 way diverter in there? I didn't but im certainly not technical.
Also is the red capped thing at 18seconds some sort of blow off valve to prevent airlocking etc? If that was set incorrectly could that be causing the problem?
I'll list out what it said below. Though first worth mentioning I set the A2 to 0 and it still did the jumping from 20 to 80% thing once it reached target temp on the boiler of 80'c. So i've turned it back off now. the below is the read outs all whilst there's no CH demand.
A1 - 203
A2 - 0
A3 - 100%
A4 - this wasn't in the menu
A5 - 45.8'c
A6 - 0
A7 - this wasnt in the menu
B3 - this wasnt in the menu
B5 - this wasnt in the menu
B7 - this wasnt in the menu
B8 - 0
C1 - 0.0
C2 - 0
C4 - 3 dotted line (not fitted)
C5 - this wasnt in the menu
C6 - 1.6bar
D1 - this wasnt in the menu
D2 - this wasnt in the menu
D3 - this wasnt in the menu
D4 - this wasnt in the menu
D5 - i have a setting for this on the boiler but its not in the manual anywhere.
Ensure you don't remove any casing that might compromise the boiler casing gas sealing.
If you follow the boiler flow pipe back you might see where the flow temperature is attached, if so, take your own reading as close to this as possible and compare it with the displayed flow temperature.
I wouldn't run the boiler at that 80C just now. Suggest 70C. House should still heat up eventually.
A1 - 203
A2 - 0
A3 - 100%
A5 - 45.8'c
A6 - 0
B8 - 0
C1 - 0.0
C2 - 0
C6 - 1.6bar
Can you follow the menu instructions in post 63 to see can you get those other readings.
If you can't access those values then OK.
Were you able you located the position of the flow temperature sensor?
Generally in the region of 50-75% output id say.
when I fire it up it starts low % and gradually creeps up but then as it hits the target flow it stays around 50% ish.
that said i have noticed many times it'll overshoot the target, turn off the burner for 1-2mins then resume, when it resumes it'll start at a very low output % again, around 20% and creep up until back to target, then stay at target at around 45-50% output.
Feeling the boiler outlet directly beneath the boiler, photo attached. .. Left read out was flow, right read out was return. But thermometers aside even to the touch there was a massive difference between boiler lcd temp and outlet temp.
Comparatively (and I know this is silly to say) but we have a 40kw conventional boiler upstairs and with that, you turn it on, and the temperature of the flow pipe of that one is always pretty consistent with the LCD read out. Leading me further to believe something is wrong with this downstair one that we're discussing.
Slight hiccup??
The pipe where the 24.7C sensor is attached to is the GAS inlet I'm pretty sure and the Boiler Return is most certainly the one with the expansion vessel attached, so might learn something further when/if you move that sensor.
Slight hiccup??
Ah, I see what you mean… no, the 24.7 sensor display is in the middle but it’s metal sensor is inside some lagging wrapped around the return pipe below where the exp vessel is.
I thought the "gas supply" was a bit on the hot side allright at 27.6C.:giggle:
I think you're next move will be to try and convince WB to revisit (under warranty) so maybe supply them with some info which "proves" that the flowtemp cannot be 15C+ higher than your readings.
Suggest, returning the target temp to 70/75C or wherever it was before you increased it to 80C. Wait until the boiler is running constantly at a steady output for say 10 minutes, note the displayed boiler target&flow temperatures, note the % boiler modulation, note your flow&return temperature readings. Also, as proof that the boiler is outputting what the % modulation is displaying I would, during this steady running period, take a snapshot of the Gas Meter and exactly 3 minutes later, to the very second, take another snapshot, the boiler output (kW) can then be calculated pretty accurately.
Edit: You did do this gas meter tests last month so perhaps no need to repeat but migh help convince the WB people.
Hi all. I’ve just joined this forum because I have EXACTLY the same problem with the same WB boiler as GeddeMortgage has been describing and came across this discussion whilst searching on-line for information. Much of what has been said above has also been coming out of my mouth almost verbatim over recent days! I will set the scene as briefly as I can but then I do have one idea/question to raise that hasn’t been mentioned so far.
My boiler is a 30kW Greenstar 8000 Style system boiler that was installed in mid-2022. It is set to 20kW maximum output and runs central heating with about 14kW of radiators and also heats a domestic hot water cylinder. It doesn’t have an internal diverter valve but there are three external motorised valves for the hot water and two heating zones. We don’t normally heat the DHW and run the heating at the same time, so my issues relate mainly to heating operation.
Like GeddeMortgage, I was noticing that despite the boiler being set to 70C, radiators were rather cool and slow to heat the house, so I used my Bosch IR thermometer (with black tape on pipes!) to check actual flow temperature at the pipe just outside the boiler and at input to radiators; lo and behold, only 50C whilst the service menu display on the boiler was showing HEx and flow temperatures of 70C or just above. How could this be the case?!
Trying to keep the story short, my accredited installer said he had only seen this once before and replacing the boiler flow temperature sensor had made no difference. He advised me to email the details to WB Technical Support, who responded immediately purely with advice to arrange an engineer call-out, as it was probably a flow sensor fault (which I somewhat doubted given my installer's experience and the fact that the displayed HEx temperature always closely tracks the displayed flow temperature).
On arrival, the engineer agreed there was an obvious discrepancy between the display and the actual flow temperature leaving the boiler and arriving at nearby radiators. He said he had never seen the issue previously and suggested that the 20C temperature drop was occurring between the flow pipe exiting the HEx and the outside of the boiler (ridiculous, as pointed out above!) but then had to admit that the pipe exiting the HEx was no hotter. He therefore replaced the flow temperature sensor, the control panel and the control unit but with no improvement. He cast doubt on the accuracy of my IR thermometer despite this having been calibrated but I have now used three different types of thermometer, which all confirm the same.
His final ‘solution’ was to set everything to maximum (boiler kW, pump pressure, etc, with modulation restricted to 80%-100% range, suggesting high resistance in the heating circuits. This, however, caused increased noise from the boiler and at radiator valves.
On the face of it, the boiler appears to be lying about the flow temperature, thus limiting its heat output to about 9kW maximum when radiators are calling for 14kW. I could give a lot more detail but it would repeat GeddeMortgage's observations.
However, I have now discovered that the external ABV is allowing flow at all times, thus returning hot flow water to the return side of the boiler. (Our ABV is fitted across flow/return pipes near the hot water cylinder but before the motorised valve, so giving a 22mm pipe circulation loop about 10m long.) So, although I have no explanation for the flow temperature display issue, I am wondering whether the continuous ABV circulation (even at 10% pump modulation) is elevating the temperature of the return water and thus limiting the amount of extra heat the boiler can then add? Alternatively, I guess this could be viewed as the ABV short-circuiting the heating circuits and depriving them of their flow? It would appear that the ABV opening pressure may be set too low - even below 100mb?
So, GeddeMortgage, you are not alone! But we still seem to be without a solution? Any further thoughts most welcome!
A ABV won't work with a modulating circ pump, see if you can have a bypass through a towel rad or similar, ie somehere where the flow is not stopped when the zone valves shut when the boiler shuts down, in any case suggest setting the ABV around (4M) and monitor the % boiler modulation in the menu, as you probably know, just multiply the % modulation X 30 to get the boiler output in kW. Or failing that, as a temporary measure set the cylinder stat to say 70C and then just manually latch open its motorized valve but don't run the boiler at a more thn 65C target flow temperature, ( but still set the ABV to that 0.4). Run the boiler then for as long as you require and take some readings/observations. Suggest also after taking some readings, change the pump to a setting that allows you to set the speed manually and increase it to say 85%, if only constant pressure is available, set it up to its max of 450mbar (4.5M) or whatever.
Maybe easier to just increase the pump speed first & increase the ABV setting to 4/5M, don'y do anything else with HW cylinder settings etc and take a set of readings as per post #63, especially (1).....A3,A5,A6,b8&C2.
Here is a thread with this same issue on another forum, looks like WB have an issue with these boilers….