543.7.1.3 (iii) para 2 (in the DPC at least)
Also I would draw to your attention the last sentence in that paragraph.
what is the logical explanation for the possible existence of yet another individual protective conductor formed by the protective sheath, armour or wire braid of the cable? Surely it can't mean that the conductor in the cable is one cpc, and the armour etc is the 2nd?
Would that then mean a RADIAL socket wired in 4mm swa,with both ends glanded properly, would automatically become a high integrity socket,I would suppose the back box socket link would have to go in a seperate earth terminal also.
I agree with ban, although two wires leave the mcb, after the first socket each way, where would the 1st and 2nd conductor end, I would say it is one conductor, any volunteers hold one end while someone meggers the other.
With a ring, rather than saying it is one conductor,I would say there was two current paths and in the event of one failing, there would still be the second path for safety.
Although that conductor is 1.5mm, you have effectively now got 3mm of cable at the socket.
With high int, if one wire came adrift that 3mm would reduce to 1.5 mm.
And by sharing the current path each way, the cable size for the live conductors can be reduced, the load on each leg of the ring, as we all know varies , dependant on where on the ring it is applied.
By loading near the centre, the cable is generally ok, as the ring would then be acting LIKE two cables in parrelel, so each current path would be balanced.
IMO
One socket, two cables from source is two cables in parallel = 2 cpc conductors
More than one socket , two cables from one source is a Ring= 1 cpc conductor