Morning All,
Can anybody advise on the this.
I have 1 set of 6no 240v LED spots that are not working. The lamps are 2 way switched by switches at different sides of our dinning area (1 of these is a dimmer, Varilight, trailing edge).
If it comes to it that we need to access cables, this will mean either pulling the fittings from the ceiling (cosmetic damage to the plasterboard) which doesn't guarantee access to the correct area or lifting the *sighs* T&G flooring in the room above, currently the nursery to our 7 month old twins.
Questions:
Thanks in advance.
Can anybody advise on the this.
I have 1 set of 6no 240v LED spots that are not working. The lamps are 2 way switched by switches at different sides of our dinning area (1 of these is a dimmer, Varilight, trailing edge).
- Everything else on that circuit is working OK.
- I have have tested the flex to the lamps with a tester stick, no power.
- I have checked the connections in the switches. All seem OK.
- I have tested the voltage across the switches - Common and L/L1 and I have 240v across the switch. The voltages moves from L to L1 or vice-a-versa as I would expect if I toggle the other 2 way switch.
If it comes to it that we need to access cables, this will mean either pulling the fittings from the ceiling (cosmetic damage to the plasterboard) which doesn't guarantee access to the correct area or lifting the *sighs* T&G flooring in the room above, currently the nursery to our 7 month old twins.
Questions:
- Is there anything else I can do/check look for a fault?
- I'm able to lift the T&G if I have to. Any tips for getting the light fittings out of the ceiling with minimal damage?
- Any other suggestions on next steps?
Thanks in advance.