18th Edition Changes

Joined
11 Jan 2004
Messages
47,160
Reaction score
4,130
Country
United Kingdom
Are there any changes to bathroom zones in the 18th?

The reason I ask is that my lad has just bought a house and due to me being not trained to the latest regs, not insured and not having certificated test equipment, he's getting a local spark to quote for work.

Three of the things the spark is unhappy with are the light fitting in the bathroom which he says is in Z2 and has an unsuitable IP rating.

The fitting is a metal plate with a screw on glass cover, very like this:
Screenshot_2026-10-02-11-01-05-526_com.android.chrome.jpg


The fitting may slightly overlap the bath, but the ceiling height is 235cm.

If the ceiling height was lower, it would be Z1, not Z2 anyway, as the fitting is on the edge of the bath, if you draw a line up to it?

The second is a surface mounted switched FCU over the bath that is above 2.25m

Yes, I suppose you could stand up in the bath and operate the switch, but technically it is outside the zones.

The third is a pull cord for the light which my lad wants replacing. I haven't measured it; it may be in Z2 or it may be > 600mm from the edge of the bath. But still, the ceiling height is 235cm.

The spark wants to get rid and put a wall mounted switch outside.

I assume that 2.25m is still the cut-off point for the end of the zones.

If it is still current, why is the spark antsy about these three things that he says are not compliant?
 
Last edited:
Not sure if this is any use, it's from the on-site guide blue book
 

Attachments

  • 20261002_122356.jpg
    20261002_122356.jpg
    501 KB · Views: 43
  • 20261002_122405.jpg
    20261002_122405.jpg
    617.6 KB · Views: 40
  • 20261002_122410.jpg
    20261002_122410.jpg
    412.2 KB · Views: 41
The only change to 701 in Amd 4 is that 'birthing pool' was removed from the scope.

Although there are other changes indicated in the margin, they are all nothingburgers, such as changing 'rms' to 'RMS', and '2.5m' to '2.50m'
 
Thanks everybody, especially pete and CF for copying the latest regs and OSG for me.

I must admit I've come across a few since the 17th that say, oh you've got to have an IP65 fitting in the bathroom or you have to have fire rated down lighters everywhere, all circuits must be RCD-protected, plastic consumer units must be changed etc...

I even had one guy arguing with me point blank that 3036s were "illegal" now.
 
Yes Myths always abound whether by missunderstanding or devious intent.
Can I just add ref the zones - the item must be outside the zones, not mounted slightly outside but with some of the item itself being within the zone slightly, I would not bother about a totally plastic cover encroaching a bit etc but a lamp and fitting within might be different risk.
I`m still waiting to see if someone puts longer legs on a bath if the still count the height from finished floor level rather than bath basin level where a person would stand. ;)
 
I suppose I should ask someone to mount a bath on six inch wooden blocks on the floor, that will cause a row!:LOL:
 
I would think if the regs wanted the 2.25m to count from the bottom of the shower tray or bath, they would make it so, but that would make life very difficult as some baths are stepped up, some baths for the disabled are raisable, so the only sensible thing is to make the floor the point of reference.
 
Yes - the point I was making is that you pick a dimension X that aperson may be stood in the bath and touching and able to touch a light fitting then you calculate the max dimension the bottom of the bath would be from the floor and add them together and you get a dimension that puts all light fittings out of normal reach.
If that works out at 2.25m then all well and good youve solved it - unless someone makes a bath that has extra long legs or mounts it on blocks then you need to add an amount to compensate for that because it effects the reach of the touching.

Some folks do the strangest things - example - yers ago I thought "Who in their right mind would be so stupid as to stand hot, nasked and sweaty, in a bath full of water and with a fillament lamp in hand attempt to fit it in a batten lamp holder whether checking or not that lampholder is live at the time?"
Apparently some idiots did such!

Charles Darwin had some remedy!
 
Yes - the point I was making is that you pick a dimension X that aperson may be stood in the bath and touching and able to touch a light fitting then you calculate the max dimension the bottom of the bath would be from the floor and add them together and you get a dimension that puts all light fittings out of normal reach.
If that works out at 2.25m then all well and good youve solved it - unless someone makes a bath that has extra long legs or mounts it on blocks then you need to add an amount to compensate for that because it effects the reach of the touching.

Some folks do the strangest things - example - yers ago I thought "Who in their right mind would be so stupid as to stand hot, nasked and sweaty, in a bath full of water and with a fillament lamp in hand attempt to fit it in a batten lamp holder whether checking or not that lampholder is live at the time?"
Apparently some idiots did such!

Charles Darwin had some remedy!
The only problem with that is peoples height and reach can vary enormously
 