It's still 2 x 13A, 26A in total. Same as a double socket.
A double socket outlet is rated at 13A *total*
I thought MK sockets were rated at 13A per outlet?
In any case, what's to stop somebody using a twin socket to supply a kettle and a toaster?
It's still 2 x 13A, 26A in total. Same as a double socket.
A double socket outlet is rated at 13A *total*
no, that would be fine if the first fcu is fed directly from the ring, and the second fcu is spurred from that.
but a spur can't feed the first fcu if the second fcu is spurred from that.
Why?
It's still 2 x 13A, 26A in total. Same as a double socket.
no, that would be fine if the first fcu is fed directly from the ring, and the second fcu is spurred from that.
but a spur can't feed the first fcu if the second fcu is spurred from that.
Why?
It's still 2 x 13A, 26A in total. Same as a double socket.
because you can't spur off a spur.
you can't, for example, spur off a ring to serve a single socket and then spur off that with another single socket. tho i think you used to be able to.
a spur feeding two single sockets as described is not equal to a spur feeding one double socket.
i agree in principal it's the same as a double socket, but it's not allowed as far as i know.
imo if you linked the spurs with 4 or 6 mm it would be ok, but it's not allowed as far as i know.
Due to it's location (airing cupboard) and the existing wiring, extending the ring (which is 2.5mm) isn't really an option and the existing FCU in there is definitely a spur
I thought about making it a switched fused spur then I could easily add 2 new FCUs without issue (correct cabling & load of course) but that would mean 3 boxes in there and the load cable on the existing unit would have to be dug out and extended.

Nothing in BS7671 that I know of.
There is mention of it in the OSG, and I think it is in reality what most people would do, but as long as the cable can not be overloaded then all is well.
A spur to a single socket which then supplies another single socket would limit the load to 26A on the spur cable, so would be OK assuming the cable is installed in a way that gives it a CCC of >26A
Personally I wouldn't do it, but it does not contravene any regulation.
Is there anything in BS1363 that relates to total loading of a double socket?