I would suggest your issue is volts drop, basically the resistance of the cable feeding the strike, is so high, the voltage is being lost within the cable itself. That is easily confirmed, if you check the voltage at the source end, when the release is pressed, and it shows an adequate voltage.

The fix, is to install a larger diameter cable, or you could try doubling up the one you already have.

I’ve double checked readings at camera doorbell. Supply comes from video monitor and is almost 24v (see pic). However, when activated, the output from here is 2.4v (see pic). The strike - 3m cable run - also receives 2.4v, no drop.
 

Attachments

  • IMG_5700.jpeg
    IMG_5700.jpeg
    757 KB · Views: 10
  • IMG_5703.jpeg
    IMG_5703.jpeg
    790.8 KB · Views: 10
I’ve double checked readings at camera doorbell. Supply comes from video monitor and is almost 24v (see pic). However, when activated, the output from here is 2.4v (see pic). The strike - 3m cable run - also receives 2.4v, no drop.
The strike will only have the correct voltage when you activate the door release …are you measuring the voltage when you activate the door open button on your monitor ? …also try it with the release disconnected it won’t be voltage drop on that cable at that distance ….more than likely you have burnt out the coil putting 24v dc into the lock release coil …
 