Whilst I agree with you that 6A would be more than enough, I'm sure that some people would say that the MCB is there only to protect the cable, so that if the cable's CCC is no less than 20A, then "why not?" a 20A MCB!Why is the boiler on a 20 amp MCB? 6 amp would be more than adequate.
Whilst I agree with you that 6A would be more than enough, I'm sure that some people would say that the MCB is there only to protect the cable, so that if the cable's CCC is no less than 20A, then "why not?" a 20A MCB!
Kind Regards, John
Why is the boiler on a 20 amp MCB? 6 amp would be more than adequate.
Do I take it that you don't subscribe to the view that the MCB is there only to protect the cable? If you did, and given that 1.5mm² is the smallest capable allowed for a non-lighting circuit, if it were Method C (and Table 4D5, not 4D2A!), you might just as well have a 20A MCB. That's not my way of thinking, but it is a common view.Very true, but unusual all the same.
Agreed. Mind you, maybe that's a reason for the 20A MCB (and maybe 2.5mm² cable?) - so that it can be used for other things as well!To be quite honest the boiler does not need its own circuit anyway.
OK, but to use a 6A OPD to protect a cable with a CCC ≥20A is then a bit OTT - and if it was the 6A OPD you'd prefer, as I said before, you are not allowed to use a cable with a CCC anything like that low!I agree the fuse is there just to protect the cable.
There's the future to consider. Many an oven could be happily supplied by a 16A/1.5mm² 'cooker circuit', but we tend not to do that!Even so it is rather unusual for a boiler circuit to be fused at 20 amp. It could be used for other things but doesn't seem to be.
As a matter of interest .... why?I always put central heating boilers on their own circuit. It's a much better design.
I thought of that one, but addressing that obviously needs a bit more than just 'having a separate circuit'Boilers, and their associated components are a common cause of RCD faults.
I suppose so. Do you take the same approach to fridges, freezers, tropical fish tanks etc. ?Also the heating is one thing you really want to keep working if there's a fault elsewhere in the property. It's very little work to put in a separate supply. It will hopefully never be needed, but when it is, it'll be one of the best things you ever did.