Hello

Part of my kitchen refurbishment, the plasterer knocked one of the plug sockets.

I only noticed this when a socket in the living room was dead. I traced back through a loop and found this socket as the potential culprit (the ones after that did not work but the one next to it did).

The next day (in the daylight) I thought I would just look at the back of the socket and put a loose wire back.

However, there are many wires!

I asked the builder of my kitchen (who's not around for a few weeks because the supplier didn't supply all the stuff and there's nothing for him to do!!), and he advised me to get a socket with larger terminals.

I therefore bought the attached.

I went to have a look at the wires today and have noted that I have 2 earths, 4 neutrals, and 4 lives (2 red, 2 brown).

However..... There's also a unsheathed wire. Looks like it is coming from next to the brown live?

Anyone have any suggestions, or should I just contact an electrician straight away?
PXL_20260418_105932062.jpg
PXL_20260418_105014962.jpg
 
The socket you have obtained is of no use there, it can only accept 3 of each wire.

A likely solution is to obtain some of these: https://www.tlc-direct.co.uk/Products/WA405.html 5 way connectors, trim and strip the existing wires so they can be connected with those connectors flat against the back of the box, and add 3 short additional lengths of wire from those to the new socket. Additional earth sleeving will be required, and there is a grommet missing from the hole in the lower left of the box. The fixing lugs will probably need be rethreaded once the plaster has been scratched out of them.
 
I couldn't find a face plate with more terminals than that?!

More common is a single terminal, for all of the wires to go in, rather than three individual terminals.

I would be questioning the need for there ever to be four wires, at one socket, and be trying to trace them. Two wires suggests a socket is on the ring. Three would suggest a socket on the ring, with a spur. Four might suggest a socket on the ring, but with two spurs, which is not to regulations.
 
Two wires suggests a socket is on the ring.
...or on a radial circuit.
Three would suggest a socket on the ring, with a spur.
... or a socket on a radial circuit with a branch/spur
Four might suggest a socket on the ring, but with two spurs,
... or a socket on a radial circuit with two branches/spurs
which is not to regulations.
Not to which regulation? - I don't think you will find one which prohibits two spurs/branches originating at the same place.
 
I'd want to test the wiring first, the 2 'new' colour cables could be an extension of a ring rather than spurs for example, connecting all the wires into the socket would then be incorrect.

You could fit 5 2.5mm cables in the older Crabtree sockets, not that I'd ever do that, before they 'improved' the design. You can barely fit 2 now...
 