This has been raised on another forum, and I don't really have an answer, we are told to retain the type tested status that a consumer unit should only be fitted with items authorised by the manufacturer which in real terms means items made by the same manufacturer. .... So if the blanks are push in type, even if you can remove them without a tool then you can't replace them with another manufacturers blanks ...
For a start, I don't know if/where there are any specific requirements in relation to the nature and scope of 'type testing' of CUs (certainly not in BS7671), or whether manufacturers can simply 'do their own thing' but, not having seen such requirements (if they exist) I am far from convinced that the 'type testing' undertaken will necessarily involve any 'tests' which are of any relevance to 'blanks'. The only specific reference to 'what is tested' in BS7671's definition is (understandably) ...
BS7671 said:
... an assembly of one or more fuses, circuit-breakers, residual current operated devices or signalling and other devices proven during the type-test of the assembly as suitable for such use...
However, that is not necessarily an exhaustive list, so it doesn't really help.
More generally, I wonder whether the belief that "domestic installations must have ('type-tested') Consumer Units" is perhaps another example of 'over-interpretation' of the regs?
I may (well
) be missing it, but I'm not aware of anything in BS7671 which explicitly requires that DBs in domestic installations have to be ('type tested') "Consumer Units" (as defined). Perhaps the closest appears in the infamous 'non-combustible' reg, which says:
421 PROTECTION AGAINST FIRE CAUSED BY ELECTRICAL EQUIPMENT
... 421.1.201 Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall: ... <silly 'non-combustible' requirements > ...
... and, since I don't know what (if anything) BS EN 61439-3 has to say about 'type testing', cannot be sure what it means/implies. The only other (often cited) reference to such matters is the reg which relates exclusively to the breaking capacity of devices, which says ...
536.4.201 Fault current (short-circuit) ratings. ...
The relevant fault current (short-circuit) rating of the assembly should be equal to or exceed the maximum prospective fault current at the point of connection to the system. .......... For an installation with a 230 V single-phase supply rated up to 100 A that is under the control of ordinary persons, switchgear and controlgear assemblies shall either comply with BS EN 61439-3 having a suitable fault current (short-circuit) rating for the maximum prospective fault current at the point of connection to the system or be a consumer unit incorporating components and protective devices specified by the manufacturer complying with BS EN 61439-3, including the 16kA conditional short-circuit test described in Annex ZB of the standard
However, this is merely a dispensation which allows ('type tested') CUs in certain domestic installations to have devices with lower breaking capacities than would otherwise be the case (per first sentence of 536.4.201). I therefore don't think this reg compels a domestic installation to have a (type-tested) CU.
I therefore wonder if I'm missing something - since, as above, it seems to me that the regs might well allow a domestic installation to have a DB which was not (or did not remain) a ("type tested") CU, provided only that it contained devices of adequate breaking capacity. Even if that were the case, 421.1.201 would presumably still require the DB to be 'non-combustible', because I imagine that it would qualify as a "similar switchgear assembly".
[In passing, as I've noted before, one could say that 536.4.201 does not actually apply to my installation because, unusually for a domestic installation, although it is "under the control of an ordinary person", it is a 3-phase supply
]
Kind Regards, John