Borrowed neutrals identifying where the error is?

Discussion in 'Electrics UK' started by ericmark, 5 Sep 2019.

  1. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    18,106
    Thanks Received:
    1,686
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    I have had a new consumer unit fitted, all seemed to work OK until night came and then lights tripped, I will guess until the two security lights were energised there was not enough current drawn as LED's don't draw much.

    So found in the hall behind the 4 gang intermediate switch there are 4 black wires in a connection block and removing one stops hall lights working and stops the RCBO's from tripping, I will guess since hall lights on the wall they have been wired different to rest, but there is the standard red, yellow, blue going to two switches so there seems no reason why it needs borrowed neutral to work.

    The consumer unit is not even in the house, so not easy running outside to reset or on/off and the RCBO do not switch neutral so trying to think of a way to test to find what does what.

    I can take the easy way out and combine upper and lower floor lighting, but I must be having a senior moment just can't think how to correct the problem. Can't find clamp on and it would not measure 30 mA anyway.
     
  2. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    36,841
    Thanks Received:
    4,124
    Location:
    Retired to:
    Country:
    Portugal
    Doesn't it only require 4 - 7 Watts if it is a borrowed neutral?
    Wouldn't a borrowed neutral cause the other circuit RCD to also trip - if more than 4 - 7W?

    Shouldn't there be 5 (or 6)? If so, which one is missing?

    Ok. It would, wouldn't it?
    Are you now saying that both RCBOs are tripping?

    Do you mean only the RBY to two of the switches?
    That still leaves the other two? So there might be the correct number of neutrals.

    You could buy one that does.
     
  3. Sponsored Links
  4. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    18,106
    Thanks Received:
    1,686
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    One neutral but two lines, the hall bridged to wrong line.
     
  5. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    18,106
    Thanks Received:
    1,686
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    Yes it did, lost all lights
    There were two three core and earth and four twin and earth not wired as expected.
    Yes
    It seems there were two line feeds, one from a triple and earth, the other from a twin and earth, the upstairs lamp from triple and earth and outside lights from twin and earth and the supply for the hall lights had been taken from triple and earth instead of twin and earth, once swapped all worked.
    Yes I could, however then I have to wait for it to arrive, my error was thinking borrowed neutral how do I connect to correct neutral, where in real terms it was borrowed line, only had to move one wire, but finding which wire to move, entailed over 5880 steps, was not wearing watch to start with, consumer unit in flat under main house, no direct connection so out back door around outside of house and down a level to flat under house every time I wanted to turn power off/on. Not all bad, think I have lost 1/2 a stone!
     
  6. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  7. Sponsored Links
Loading...

Share This Page