Bypass valve
Here is a thread with this same issue on another forum, looks like WB have an issue with these boilers….
Indeed, and what is very annoying is that even when the boiler output is well above its minimum output that the flow temperature can be 2 to 3 deg higher than the target flow temperature even under steady demand conditions, completely unacceptable, IMO, because the burner trips (shuts down) at target temp +5C, if a heating zone is shut down then its very likely that the flow temp will rise by a few degrees and will trip the burner, leading to recycling.
Thank you Johntheo5 and Mister Banks for your replies.
Firstly to Mister Banks, thank you for pointing me to the thread on Buildhub, which I see is not only on the same issue but was actually started on 15th December by the same person (GeddyMortgage) about the very same boiler and issue as this thread here on DIYnot.com has been discussing. One can see that much of the description and also the pipework diagram and photos are the same as on this thread. His last post here was on 16th December and he signs off his initial post on Buildhub as ‘Ged’. Thus he appears to have switched from this forum to Buildhub around 15th/16th December.
That said, I have read the whole of the Buildhub thread, which eventually reveals that the cause of all his problems (identical to mine) with actual flow temperature being well below that being sensed and displayed by the boiler was a scaled or clogged HEx. As soon as this was diagnosed and replaced by a senior WB engineer, the actual flow temperature increased to match the indicated one.
And on thinking this through further, I can see how a scaled/clogged Hex can explain all his and my observations, including the fact that the discrepancy is not constant but can vary between about 10C and 20C. In my own case, I would not be that surprised if my Hex were to be clogged, as existing pipework and some retained radiators were not cleaned before the new boiler was installed (despite the old system having been open vented and out of action for 17 years after the old boiler and pump were removed!). However, cleaner was run for a week in the completed new installation, which does have a strainer and a magnetic filter in the main boiler return. These have been cleaned at each annual service since.
So it looks as if I will have to get WB back again, with a view to having the HEx replaced. The previous engineer did say that would be the next thing to try.
Turning to Johntheo5’s reply regarding my ABV question, I understand that, with a modulating pump, we do not need an ABV during normal operation but, because all circuits (two heating + DHW) are controlled by motorised valves, we do need one for pump overrun when all three valves are closed at the end of a heat demand. There is no unvalved circuit to a towel radiator or similar. But the ABV should be closed during all normal operation (as is made clear in WB Technical Bulletin 0159 (03/2022), which also specifies the need for a pump overrun ABV).
I am quite sure that my ABV is passing flow during normal operation, as the 10m pipe loop it uses is hot throughout at virtually the same temperature as the concurrent heating flow. Presumably, this additional hot water being added to the return flow will have some negative effect on boiler control? So I will do as Johntheo5 suggests and increase the ABV pressure setting until the unwanted circulation stops; hopefully it will still open when needed for pump overrun.
Thank you both again for your assistance. I will post again when I have further news.
There's still a problem, maybe new, since the new HEX was installed, with the (a) dT between the target and flow temps even under steady firing conditions, but maybe sorted since engineer was scheduled to come back on the 16th.
Thank you Johntheo5. Yes, I followed all that on the Buildhub thread but am not so worried about the indicated flow temperature sometimes being a bit above the set flow temperature. My big concern is the actual flow temperature being unable to reach the set or indicated flow temperature by as much as 20C and the limitation that puts on the boiler's actual heat output. His problem like this did seem to be completely solved by the HEx replacement on 22nd December.
But I also have my problem with the ABV! With the boiler pump map set to constant pressure option 1, which equates to 150mb, I cannot stop the circulation through the Honeywell DU144 ABV, even when I wind it all the way to setting 0.6, which equates to a pressure of 600mb to 1000mb, depending on flow rate. Surely that should stop the flow? Seems like the valve must be faulty or stuck open. I was suspicious to start with, because it was passing flow at the installed setting of 0.3, which should not have been happening at pump setting 1 anyway.
What I do notice having taken the valve to setting 0.6, is that at any lower setting the knob just feels loose, as if it is not doing anything. Is that normal or does it also point to a faulty valve?
Thank you again.
Looks very like a knackered ABV, easy enough to confirm.
Put the pump map to 1....150mb
After a few minutes read off the pump modulation in 1-C2 %
Then go to pump map 3...250mb
Again read off the pump modulation
Ensure ABV at index 6
Thank you Johntheo5. I will do that and post back. Meanwhile, glad to hear you have the same suspicions as me!
OK Johntheo5 ……
ABV set to 0.6 (600mb+).
Boiler started by raising room stat for one heating circuit.
Pump at 150mb; wait 5mins; Pump modulation 46% and rising slowly.
Pump at 250mb; wait 5mins; Pump modulation 63%.
Pump back to 150mb; wait 5mins; Pump modulation 50%.
Pump back to 250mb; wait 5mins; Pump modulation 63%.
Even at 150mb pump pressure and ABV at 600mb+, the whole 10m ABV loop gets hot at almost the flow temperature from the boiler. And the ABV adjustment knob still now feels loose over its whole range from minimum to 600mb, having once set it to 600mb. Only when it is rotated to the 600mb setting does any resistance now start to be felt. But it is always passing hot water.
Yes, Renew the ABV before doing anything else.
That appears to be a 7M (700mb) pump, Pump head is proportional to speed squared so pump head at 50% modulation = 700*0.5^2, 175mb and pump head at 63% modulation = 700*0.63^2, 278mb (2.78M), nowhere near index 6 on the ABV.
You might also, for interest, when the boiler & system have settled down take the following readings.
1-A5 Flow Temperature
1-A6 Target Flow Temperature
1-b2 Burner modulation
1-C2 Pump modulation
Pump map setting
Thank you again Johntheo5. Yes, that was my conclusion (before getting back to WB about the flow temperature issue and a possible HEx replacement).
I will take those readings you suggest (plus my true flow temperature measurement!) and then post back.
Time and time again...
If a new boiler is installed onto a dirty system, it will fook the boiler!
This is why manufacturers are now strict with warranty conditions... They've changed enough hex's to know what fooked them!
"Oh, but this quote for an install was cheaper!"
YES... because that quote didn't allow for a PROPER system clean, that could be proved by testing... Not just promising!!!
Thank you dilalio. We actually went for by far the most expensive quote with a personally recommended company that is Worcester Bosch accredited to the 12 year warranty level. It was also the company that instilled the greatest confidence in us after extensive discussions with several about the proposed work. I guess if they did not do the work to the standard required by Worcester Bosch, that must also be a matter that WB should address. (BTW, the personal recommendation came from a highly talented ex-Rolls-Royce aero engineer for whom the company had also done similar heating work.)
We will have to see in due course whether there is a problem with HEx contamination or not. Meanwhile, the ABV question has to be sorted.
When/if doing the above tests, can you please take one set of readings with pump speed set to 100% and another test with a pump map settings of 6, 400mb.
Thank you Johntheo5. Will do when a get a bit of time. Trying to keep all my life balls in the air! Have been in communication with my installer about the ABV ……….! (On a conventional open-vented system and boiler, I would happily dive in and change the valve myself but I’m not used to sealed systems with 'fragile' modern boilers under long warranty, so erring on the side of caution ……. though it may cost me!)
Thanks again for all your help. I'll be back soon hopefully.
Hi Johntheo5, have done the measurements and here are my results:
First set are at pump map 2 (200mb):
Target flow temperature set: 70
Indicated flow temperature: 73
(Actual flow temperature: 57)
Burner modulation: 21% (6kW)
Pump modulation: 58%
Second set are at pump map 6 (400mb):
Indicated flow temperature: 72.5
(Actual flow temperature: 57.5)
Burner modulation: 19% (6kW)
Pump modulation: 83%
Third set are at pump map 0 (proportional) with max and min both set to 100%:
Indicated flow temperature: 69
(Actual flow temperature: 56.5)
Burner modulation: 16% (5kW)
Pump modulation: 100%
Hopefully things were sufficiently settled for each set of measurements. Remember that flow water was going round the ABV loop to near the boiler return!
Thanks again!
My AWACS system must be down but didn't see your post until a hour ago, however.....
Obviously the ABV will distort things somewhat but it might seem that the HEX may not be that blocked up but of course could still have some very hard insulating type of scale build up, what is really amazing though is the dT of ~ 13C between the boiler flowtemp and your measured temps, same as other problem boiler.
Using a assumed clean HEX dP of 1.0M/16.0LPM then I come up with a boiler/rads/system/ABV bypass, flowrate of 7.52LPM..Reshead 202mb, with the 200mb test.10.76LPM..Reshead 413mb with the 400mb test and 12.96LPM..Reshead599mb with the 100% test.
Did you note the actual return temps during those three tests?
THe HEX dP + of course the system (rads etc) dP will determine the pump speed required to give any chosen residual head, 400mb in this case, below.
The second one below is with a new HEX, and (if calcs correct) a flowrate of 20.7LPM at 100% pump speed,
Forgot your one, immediately below, of course skewed a bit by the bypassing ABV.