I often quote the 2m rule, but as I think Ban pointed out in a previous thread, I think the 16th/17th does not actually mention distance. Yes, the OSG & BRG advise 2m, but it is not set in stone.
Just for amusement value, this is the history of the "2m" rule from the 14th onwards:
The 14th says,
A29.
Every stationary cooking appliance shall be controlled by a switch separate from the appliance and installed within 6 feet of the appliance. Where two SCA's are installed in one room, one switch may be used to control the two appliances provided that neither appliance is more than 6 feet from the switch.
The 15th says,
476-20.
Every fixed or stationary household cooking appliance shall be controlled by a switch separate from the appliance and placed within 2m of the appliance. Where two SCA's are installed in one room of household premises, one switch may be used to control both appliances provided that neither appliance is more than 2m from the switch.
The 16th says,
476-03-04
Every fixed or stationary appliance which may give rise to a hazard in normal use and is connected to the supply other than by means of a plug & socket complying with regulation 537-05-04 shall be provided with a means of interrupting the supply on load. The operation of the means of interrupting the supply on load shall be placed so as not to put the operator in danger. This means may be incorporated into the appliance or, if separate from the appliance, shall be in a readily accessible position. Where two or more appliances are installed in the same room, one interrupting means may be used to control all the appliances.
Anyone care to add what the 17th says? I have not got my copy to hand.
Where do you want to put yours in relation to the cooker?Is there anything in regs regarding where the switch should be located ?
422.3.15 A heating appliance shall be fixed.
522.2.2 Parts of a cable or flexible cord within an accessory, appliance or luminaire shall be suitable for the temperatures likely to be encountered. as determined in accordance with Regulation 522.1.1, or shall be provided with additional insulation suitable for those temperatures.
514.1.1 Except where there is no possibility of confusion, a label or other suitable means of identification shall be provided to indicate the purpose of each item of switchgear and controlgear. Where the operator cannot observe the operation of switchgear and controlgear and where this might lead to danger, a suitable indicator shall be fixed in a position visible to the operator.
421.4 Fixed equipment causing a concentration and focusing of heat shall be at a sufficient distance from any fixed object or building element so that the object or element is not subjected to a dangerous temperature in normal conditions.
537.4.1.1 Means shall be provided for emergency switching of any part of an installation where it may be necessary to control the supply to remove an unexpected danger.
So, to cut to the chase...
It's within the 2 meters quoted but hoped to site it on the wall at the back of the cupboard with a cut out in back panel for access
Interesting points in that there are virtually no safety devices on the gas supply.The far more dangerous gas cookers do not seem to have isolators placed to remove the gas supply in case of fire so why should electric cookers have more safety devices than a cooker with open flames? The spigot connection for the gas cooker is often where it can't be reached without moving the cooker and often one has to go outside to turn off the main gas valve.
Remember the "old rule" where if you had one hand in the sink full of water, you shouldn't be able to plug an appliance into a socket outlet with the other wet hand?
At the time (late 80's) I was told 'its in the regs'. Now, with me rewiring my typical 40's/50's semi just up from Longbridge in Brum. Technically, we couldn't have a socket in the kitchen! But it did stop me putting sockets in the bay window that contained the sink.Wonder how old that one is? AFAICT, it's not in the 14th...![]()