Earthing a metal container

Discussion in 'Electrics UK' started by Feel the power, 24 Aug 2016.

  1. Feel the power

    Feel the power

    Joined:
    24 Aug 2016
    Messages:
    13
    Thanks Received:
    0
    Country:
    United Kingdom
    Evening all, I was asked to price a job today which was putting power into a metal container, the sockets and lights would be installed using plastic conduit as the feller doesn't like galvanised conduit, the supply is already there which is a 10mm twin and earth on catinery and this is fed directly from the house which has a Tn-c-s supply, I am going to install a metal clad cu with rcbos as he doesn't want them all tripping at the same time, all I'm wondering is will it be accepted to install a TT rod on the outside of the container and connect this to the MET on the cu in the container any help would be grateful and much appreciated Thanks
     
  2. Sponsored Links
  3. securespark

    securespark

    Joined:
    11 Jan 2004
    Messages:
    37,151
    Thanks Received:
    1,290
    Country:
    United Kingdom
    Has the container got a water or gas supply via a metallic pipe?
     
  4. Feel the power

    Feel the power

    Joined:
    24 Aug 2016
    Messages:
    13
    Thanks Received:
    0
    Country:
    United Kingdom
    No it hasn't got anything it's just going to be used as a workshop so just power and lights to be installed also should mention the container is about 10 meters away from the house
     
  5. Iggifer

    Iggifer

    Joined:
    8 Sep 2011
    Messages:
    4,637
    Thanks Received:
    587
    Location:
    Warwickshire
    Country:
    United Kingdom
    T+E on catenary wire.....I'd walk away if I'd be asked to look at that job
     
  6. Feel the power

    Feel the power

    Joined:
    24 Aug 2016
    Messages:
    13
    Thanks Received:
    0
    Country:
    United Kingdom
    I know tell me about it not the best but no way of changing it unfortunately, and I didn't install it so that's another query
     
  7. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    9,927
    Thanks Received:
    1,989
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    An earth rod will do very little, considering you already have a giant metal box in direct contact with the ground.
    RCBOs are good - but only if the supply from the house does not already have an RCD. Even if the supply is just via an MCB, there will still be a problem of discrimination for short circuit faults.
    10mm T&E will have a CPC of smaller size, which will be no use for equipotential bonding on a TNCS supply.

    The overhead T&E will need to be replaced, and this should be priced as part of the work. Even without the cpc size problem, T&E hanging outside is not suitable.

    Another consideration is that metal sheds / containers are magnets for condensation, and the interior is likely to be dripping wet at certain times of the year. Equipment installed in it should be rated accordingly.
     
  8. Feel the power

    Feel the power

    Joined:
    24 Aug 2016
    Messages:
    13
    Thanks Received:
    0
    Country:
    United Kingdom
    I understand where your coming from, I wasn't particularly glad when I seen the t+e hanging but it was all ready installed prior to me going to the job and the path underneath has just been nicely tarmaced so no chance of digging that up, what are your recommendations with what I've got to work with
     
  9. Iggifer

    Iggifer

    Joined:
    8 Sep 2011
    Messages:
    4,637
    Thanks Received:
    587
    Location:
    Warwickshire
    Country:
    United Kingdom
    1. Replace the T+E with a suitable cable
    2. Don't do the job

    It's you that's going to be responsible for that cable once you connect on to it. How high up from the floor is it?
     
  10. Sponsored Links
  11. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,635
    Thanks Received:
    3,189
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    This seems like an interesting one. Without commenting on the issue of the overhead T+E feed, the container (assuming that it is sitting on the ground) presumably counts as a giant extraneous-c-p, which therefore needs to be bonded to the container's installation. If this were an 'ordinary' outhouse which had extraneous-c-ps, one of the options we would be suggesting would be to not export the TN-C-S earth to the outbuilding but, instead, to TT the container with a local earth electrode. However, in the case of the container, as you say, a rod might be pretty superfluous if the container were in contact with the ground. In that situation, if the measured resistance to ground of the container were low enough, would it be acceptable to regard it as the 'earth electrode' and therefore not bother with a rod? I suspect that one problem might be that, under dry conditions, the 'resistance to earth' of even a giant metal box just sitting on the surface might be quite high.

    Kind Regards, John
     
  12. Feel the power

    Feel the power

    Joined:
    24 Aug 2016
    Messages:
    13
    Thanks Received:
    0
    Country:
    United Kingdom
    It's a good 7 meters high well out the way of anything and nothing can pass under it
     
  13. Feel the power

    Feel the power

    Joined:
    24 Aug 2016
    Messages:
    13
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks for your reply John, it it worth installing the rod just as precaution incase of dry spells and surly if the rod is installed it would create a easier earth path if a fault was to occur within the container?
     
  14. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,635
    Thanks Received:
    3,189
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    I agree. I was really responding to flameport's suggestion that the earth rod would/might be superfluous. However, I would think that it would represent a more reliable connection to earth than would a container which could be sitting on bone dry ground.

    If you do TT the container, you need to be careful to keep the TN-C-S earth well away from it - i.e. don't connect anything to the CPC of this increasingly infamous T+E feed!

    Kind Regards, John
     
  15. Feel the power

    Feel the power

    Joined:
    24 Aug 2016
    Messages:
    13
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks John, just wondering tho how would you suggest of keeping the TT away from the CPC of the incoming supply as the CPC of the t+e feed would need to be connected to the MET of my new metal clad board or am I going in the complete wrong direction here
     
  16. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,635
    Thanks Received:
    3,189
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    If you were TTing the container, you would not connect the CPE of the T+E feed to anything in the container (and you would make sure that it could not be touched). Only the local TT rod, main bonding to the container and the connection to the local CU would be connected to the container's MET.

    ... unless someone disagrees with me, that is :)

    Kind Regards, John
     
  17. Echo the husky

    Echo the husky

    Joined:
    25 Mar 2011
    Messages:
    2,476
    Thanks Received:
    326
    Location:
    Devon
    Country:
    United Kingdom
    I'll agree with you John! Was half way through typing the same reply!
     
    • Thanks Thanks x 1