I agree that it's a bizarre standard, but why would none of the manufacturers state that their 20A DP switches could be fitted on a 32A RFC.
Maybe they fear that the switches might be used in a way that has a load of more than 20A going through the contacts, rather than just in and out of the terminals?
Ditto 32A radials, of course.
I wonder why, if they don't believe they can be used on >20A circuits they make them with terminals which can take 2 x 6mm² cables?
What about a 32A radial, would you consider it acceptable to use a 20A switch on such a circuit if there was a plugtop fuse downstream?
Define "acceptable"....
IMO it would be perfectly safe, as the load on the switch is limited to 13A.
Would it contravene the regulations because it's not what the manufacturers say you can do? I'm not so sure that the manufacturers
do say that you can't use them that way. Look at the technical specs for MK Logic, for example:
Current rating:
Connection units – 13 amp
DP switches – 20 amp
Flex outlets – 20 amp
If the 20A in the switch spec means that you can't put it on a 32A circuit to switch a load of ≤ 20A, what does the 13A in the FCU spec mean?
If someone did not explicitly ask the manufacturer about putting a switch on a 32A circuit, and instead just read their specifications, what interpretation would he place on a specification like that, reading it with reasonable skill and care?
As I have often said, if there are two ways to interpret something, and one of them introduces illogical conclusions and inconsistencies where the other does not then you ought to seriously consider if that one is wrong.