Hive dual channel receiver & with Baxi Platinum combi boiler

Discussion in 'Plumbing and Central Heating' started by Simon2018, 11 Jan 2019.

  1. Simon2018

    Simon2018

    Joined:
    11 Jan 2019
    Messages:
    3
    Thanks Received:
    0
    Country:
    United Kingdom
    E2B57CAB-20E6-402B-9317-8F6D235C5EC6.jpeg Hi

    Can anyone help me with how to wire a hive dual channel receiver to a Baxi Platinum?

    I know it should be a single channel receiver but is it still possible!?

    See attached wiring diagram for the boiler and hive

    Thanks
     

    Attached Files:

  2. Sponsored Links
  3. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    22,289
    Thanks Received:
    2,084
    Location:
    Bedfordshire
    Country:
    United Kingdom
    Dual Channel and Single Channel have different internal wiring.
    0x56.jpg
     
  4. stem

    stem

    Joined:
    20 Jul 2005
    Messages:
    5,913
    Thanks Received:
    1,259
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    It can be done but it's not very professional and you will have hot water control features on your app that won't do anything. So, I would recommend changing it for a single channel version that is specifically designed for combi's.

    With either version, if you have to open up a room sealed compartment to access the wiring terminals (with some boilers you do, some you don't) this is not a DIY job and should be done by a Registered Gas Installer (Gas Safe), who can make sure it is properly sealed up again afterwards.

    However if you can't exchange the Hive, and can access the terminals without opening a room sealed compartment, it can be connected as follows:

    The Dual Channel needs a N & L from the same 3A fused supply as the boiler. [see red circle]
    The Hive (4) 'Heating on' connects to the top terminal where the wire marked bk1 is [see green circle]

    Untitled.png

    No connection is required to the terminal where the wire marked bk2 is.
     
  5. Simon2018

    Simon2018

    Joined:
    11 Jan 2019
    Messages:
    3
    Thanks Received:
    0
    Country:
    United Kingdom
    Thank you both for your help and advice.

    What does the wire BK2 do?
    It’s marked up as 230v

    Thanks
     
  6. stem

    stem

    Joined:
    20 Jul 2005
    Messages:
    5,913
    Thanks Received:
    1,259
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    The bk2 wire provides a 230V live output for a thermostat, as the direction arrow on the boiler connection diagram shows. However, the Dual Channel Hive doesn't need this additional live as it is internally linked to its own live as Bernard's diagram shows quite nicely for you.

    Capture.JPG

    So there is no need for another live connection to the Hive from the terminal bk2 is connected to, as it already has one.

    The end result will be this:

    Capture.JPG
     
    Last edited: 13 Jan 2019
  7. Simon2018

    Simon2018

    Joined:
    11 Jan 2019
    Messages:
    3
    Thanks Received:
    0
    Country:
    United Kingdom
    Ok great thanks again for the help
     
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  9. Sponsored Links
Loading...

Share This Page