Yes.Currently there is a 9000w cooker hardwired, the by the side socket has 13A capability. I see lots of these want 45amps
Quite right but we apply what we call 'diversity' because the cooker elements will cycle on and off even when switched on.The current cooker all electric (not mine but left behind) is 9000 w (label says can go to 9800) so that's 40a min.
Plus a 13a socket.
That's 53a on a 32a circuit. Something's not right in my head.
The current cooker all electric (not mine but left behind) is 9000 w (label says can go to 9800) so that's 40a min.
Plus a 13a socket.
That's 53a on a 32a circuit. Something's not right in my head.
Exactly.What you are missing is what is called 'diversity'. A single item, might draw it's full current rating, but an oven is not classed as a single item, it has multiple rings, multiple elements and not all will usually on and drawing current at the same time - that is where 'diversity' comes in as a factor.
Likewise, your three outlets will not all be turned on and drawing a full 13 amp at the same time, so 'diversity' applies. Your 32 amps can actually support 2.25 of the three outlets drawing their full rated 13 amp load - ample.
What you are missing is what is called 'diversity'. A single item, might draw it's full current rating, but an oven is not classed as a single item, it has multiple rings, multiple elements and not all will usually on and drawing current at the same time - that is where 'diversity' comes in as a factor.
Likewise, your three outlets will not all be turned on and drawing a full 13 amp at the same time, so 'diversity' applies. Your 32 amps can actually support 2.25 of the three outlets drawing their full rated 13 amp load - ample.
I agree. As you imply (and although the guidance in the OSG does not acknowledge this) I would say that a current-limited appliance (even if a 'cooking appliance') invalidates the concept of diversity.However, I am not sure how this would apply to a hob which limits the current drawn to 13A. I would think it is likely to be 13A for much of the time with more than one ring on.
It should be it's - not its.You mean 'its plug has a fuse.'
I'm afraid you're wrong. Since, by convention, " it's " is an abbreviation for "it is", we do not use the apostrophe to indicate possession (as we normally would)It should be it's - not its. (I think. Hang on...)
So I see - just had a lesson on Google.I'm afraid you're wrong. Since, by convention, " it's " is an abbreviation for "it is", we do not use the apostrophe to indicate possession (as we normally would)
Kind Regards, John
Is it a gas hob? A UK plug can hold a fuse rated at up to 13Amps. The majority of appliances connected to them do not draw 13Amps.It's a plug in hob. 13a plug. Same for oven
Hello. No it's an electric hob, give me a moment I'll find a link (search Google for plug in hob, they are normally induction)Is it a gas hob? A UK plug can hold a fuse rated at up to 13Amps. The majority of appliances connected to them do not draw 13Amps.
Not so. It is for those who do not have a cooker supply and want to plug it in to socket circuit.One of the benefits is they are actually low power and given the situation in the world right now it's a plus, takes longer to cook but less energy
If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Are you a trade or supplier? You can create your listing free at DIYnot Local