What else do the regulations allow to be supplied by a circuit with undersized conductors?It depends whether you think "Accessories to BS1363 may be supplied through a ring..." means nothing else is allowed to be.
What else do the regulations allow to be supplied by a circuit with undersized conductors?It depends whether you think "Accessories to BS1363 may be supplied through a ring..." means nothing else is allowed to be.
Supplied through ??? How are accessories supplied?What else do the regulations allow to be supplied by a circuit with undersized conductors?
You asked:It is not a question of size wrt accessories.
So what difference does being on a ring make?What else do the regulations allow to be supplied by a circuit with undersized conductors?
...but there are two of them (2.5mm² cables).Were it not for the exemption in 433.1.204, overload protection of a 2.5mm² cable with a 32A device would be non-compliant.
Did you mean accessories to BS 1363?Is it not the case that accessories to BS7671 may be supplied through a radial circuit of similar or different characteristics?
None to the accessories - you are looking at it the wrong way round.So what difference does being on a ring make?
Of course it is.Is it not the case that accessories to BS1363 may be supplied through a radial circuit of similar or different characteristics?
And unless they are installed and used in the way prescribed in 433.1.204 the circuit would be non-compliant....but there are two of them (2.5mm² cables).
None - you are looking at it the wrong way round.What relevance has that to the accessories?
I feel you phrased the question the wrong way round.None to the accessories - you are looking at it the wrong way round.
433.1.204 does not mean that accessories to BS1363 may only be supplied through a ring final, it means that only they may only be supplied through a ring.
Analogies:
Only cyclists may use cycle lanes vs Cyclists may only use cycle lanes.
Jews may only eat kosher foods vs Only Jews may eat kosher foods.
Only sterile scalpels may be used for surgical purposes vs Sterile scalpels may be only used for surgical purposes.
Exactly - for the circuit.433.1.204 creates an exception for the circuit, and allows a ring using 2.5mm² cable and a 30/32A OPD, where the loads are not fixed and the conductors are not in parallel.
If that were so - then - why?But the only things it permits the circuit to supply are accessories to BS1363.
433.1.204 does not mean that accessories to BS1363 may only be supplied through a ring final, it means that if you have a ring using 2.5mm² cable and a 30/32A OPD you may only use it to supply accessories to BS1363.
It does mean that, it does not have to have the word only, as it is defining an exception.433.1.204 does not include the word only, therefore it does not mean only those may be supplied through that type of circuit.
That is not the case. My bet is that if you were to show such a circuit your design would be one which does not rely on the provisions of 433.1.204 to be compliant.After all, with the correct design, appliances, not to BS1363, may be supplied through a ring circuit without a BS1363 accessory.
Because otherwise the circuit might be unsafeIf that were so - then - why?
Those are very good points - it is true that as written other accessories may not be used. Unfortunately for you, as soon as you question the intention of 433.1.204 in an attempt to resolve that it becomes clear that only BS1363 accessories can be points of use.What relevance are the exceptions to the accessories such that 20A switches would not be allowed?
or junction boxes?