hello chaps, hope all is well wherever you are tonight!
was bored so thought i'd wack on a pic
was called out today to install a few downlighters, this is the incoming supply to the house, lady asked me if it looked in order, my response was 'yes'. I think it lives up to todays required standards!!!
Apart from the multitude of cobwebs, and the lack of a DP Isolation Switch that is!! The query I had was that after this juncture, the meter leads run a complete distance of 5m before they reach the CU. Isn't the max distance 3m by code? or with 3m (+) runs, implementation of a second 100A isolation switch??
was bored so thought i'd wack on a pic
was called out today to install a few downlighters, this is the incoming supply to the house, lady asked me if it looked in order, my response was 'yes'. I think it lives up to todays required standards!!!
Apart from the multitude of cobwebs, and the lack of a DP Isolation Switch that is!! The query I had was that after this juncture, the meter leads run a complete distance of 5m before they reach the CU. Isn't the max distance 3m by code? or with 3m (+) runs, implementation of a second 100A isolation switch??