    Evening all, apparently I have the wrong voltage going to my boiler, it has 238v Live to Neutral, 78v Live to Earth and 63v Neutral to Earth???

    Can anyone tell me what the problem could be???

    Thanks...
     
  2. Sponsored Links
  3. RF Lighting

    RF Lighting

    Joined:
    31 Mar 2006
    Messages:
    19,986
    Thanks Received:
    1,351
    Location:
    Leeds
    Country:
    United Kingdom
    More than likely it's a missing earth.
     
  4. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    9,417
    Thanks Received:
    1,841
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    Probably the earth is not connected, or less likely, the neutral is not connected.
     
  5. Crezzer

    Crezzer

    Joined:
    5 Jul 2010
    Messages:
    336
    Thanks Received:
    63
    Location:
    Essex
    Country:
    United Kingdom
    There's a live, neutral and earth coming into the fused spur that the boiler is fed from?? So is it likely the the earth isn't making its way back to the board??
     
  6. Sponsored Links
  7. EdwardCurrent

    EdwardCurrent

    Joined:
    29 Apr 2007
    Messages:
    907
    Thanks Received:
    22
    Country:
    United Kingdom
    Hello Crezzer.
    Is the boiler on its own dedicated radial circuit ? Or fed off an existing circuit please ?
    Ed
     
  8. Crezzer

    Crezzer

    Joined:
    5 Jul 2010
    Messages:
    336
    Thanks Received:
    63
    Location:
    Essex
    Country:
    United Kingdom
    I would say it comes off the ring main, the twin and earth disappears through the ceiling and there's no seperate MCB for it.....
     
  9. EdwardCurrent

    EdwardCurrent

    Joined:
    29 Apr 2007
    Messages:
    907
    Thanks Received:
    22
    Country:
    United Kingdom
    Hi,
    Job number one is to find out which circuit it is 'on', and then where, and how it has been connected. Hopefully it wont be a concealed junction box, but from a 'local' socket. ;)
    Good Hunting and work safe.
    Ed
     
  10. baldelectrician

    baldelectrician

    Joined:
    27 Jul 2005
    Messages:
    519
    Thanks Received:
    7
    Location:
    Ayrshire
    Country:
    United Kingdom
    Be careful

    Was at one last week where the boiler guy identified reverse polarity.

    Turned out to be a L-E fault on the hob and a bad earth- 58 Ohms.

    All the house metal work (sink, radiators, boiler, hob. oven) was at 240V or thereabouts

    This has the potential to be real saftey issue. It requires checking out quickly

    You should use a competent person for the work, links below
    In Scotland:
    Individuals registered;
    http://www.sbsa.gov.uk/register/ListAC.asp
    Companies
    http://www.sbsa.gov.uk/register/SearchRegCo.asp?T=Construction
    In England and Wales:
    http://www.competentperson.co.uk
     
  11. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page