Yep - "to" should be "no". Now corrected. Thanks.Just to be sure: is there a typo?
Kind Regards, John
Yep - "to" should be "no". Now corrected. Thanks.Just to be sure: is there a typo?
Surely, the fact that it is deemed Class I is only relevant when the supply is such that the Class I precautions need to be considered.I am saying that it is Class I (and hence only considered safe if its exposed-c-ps are earthed) BECAUSE it does not qualify as Class II.
You might as well say the same if the so-called Class I item were supplied by a 12V supply.Since, with a floating supply, earthing the exposed-c-p does not provide any additional protection, if a Class I item with an earth-referenced supply is not regarded as 'safe' unless the exposed-c-p is earthed, then nor can it be 'safe' with a floating supply, even if the exposed-c-ps are earthed.
Well, as I've said, the "Class I precautions", per se, appear to be useless when the supply is floiating.Surely, the fact that it is deemed Class I is only relevant when the supply is such that the Class I precautions need to be considered.
I haven't looked recently, but seem to recall that the regs are a little silly in not making exceptions for ELV in relation to these matters.You might as well say the same if the so-called Class I item were supplied by a 12V supply.
Yes, generally the idea is that an appliance should be safe under "single fault conditions". Failure of basic insulation would be considered a "single fault".The point I was making to Sunray was that if an item is designated as Class I, the implication is surely that the "basic insulation" (plus "additional insulation" if present) is not considered adequate to provide the required degree of protection against electric shock
bonding all the metalwork in the vicinity of a supply together with bonds that have sufficiently low impedance (ideally significantly less than the source impedance of the supply) will limit the touch voltages that can develop between those parts.(b) is irrelevant
No one knows; it is like a plastic switch or socket - nothing?This really brings me back to a question that I must have asked dozens of times, without getting an answer - if an item does not have "double or reinforced insulation" (hence cannot be Class II) and also has no exposed-c-ps (hence cannot be Class I)m, then "What is it?" (maybe 'not allowed'?).
I do not disagree. On the contrary, I do not think it should be 'earthed'Remember that most of these recent exchanges resulted from Sunray expressing 'shock' when I suggested that if a supply is (and remains) 'fully floating', that nothing is then achieved by earthing the exposed-c-p of a Class I item connected to that supply. Do you disagree with that?
Same reason why yellow sockets are marked line and neutral not line 1 and line 2.Another interesting question. Why are the 2 live conductors in an IT system called 'L' & 'N' ?
I haven't read the standards for commercial grade appliances (I have read the medical standard IEC 60601 but it was quite some time ago) but my understanding is that the basic idea is.This really brings me back to a question that I must have asked dozens of times, without getting an answer - if an item does not have "double or reinforced insulation" (hence cannot be Class II) and also has no exposed-c-ps (hence cannot be Class I)m, then "What is it?" (maybe 'not allowed'?).
Indeed.Yes, generally the idea is that an appliance should be safe under "single fault conditions". Failure of basic insulation would be considered a "single fault".
Are you suggesting that a failure of the insulation which allows ones to touch both sides of a a floating supply (e.g. both terminals of a lampholder) constitutes more than a single fault?But a floating supply (of sufficiently low leakage) is single-fault safe by design.
Indeed, but we're not talking about bonding different bits of metalwork to one another but, rather, of bonding the exposed-c-p of one (Class I) item to earth. That will therefore only limit the touch voltage between that exposed-c-p and 'something earthed' - which really cannot arise (with low enough path impedance to be important) when the supply is, and remains, floating.bonding all the metalwork in the vicinity of a supply together with bonds that have sufficiently low impedance (ideally significantly less than the source impedance of the supply) will limit the touch voltages that can develop between those parts.
Quite so - and, as I have said, I think a problem could only arise if one of the multiple faults had the effect of rendering the supply no longer floating.With a floating supply this only really becomes relavent when you consider multiple fault conditions.
Fair enough, but I was thiunkiung primarily about domestic / consumer products, anyway.I haven't read the standards for commercial grade appliances (I have read the medical standard IEC 60601 but it was quite some time ago) ...
That is also my understanding.but my understanding is that the basic idea is.
Class 0: protection by basic insulation only, not single fault safe, generally not allowed anymore.
Class 1: protection by basic insulation in combination with metalwork connected to a protective conductor.
Class 2: protected by double (basic plus supplementary) or reinforced (a single layer of insulation that provides protection equivalent protection to basic and supplementary insulation combined)
Indeed - but, as above, what if there is no metal (to earth) at all - it surely can't them be regarded as Class I?An earthed metal part can be part of the protection strategy even if it's not directly exposed to touch.
You pre-empted a comment I was about to make - namely that plastic accessories obviously cannot be Class I and do not bear a Class II marking, again leading to the "What are they?" question. However, as you say, one assumes that they do have what would, in other contexts, be regarded as 'reinforced insulation' so are conceptually 'Class II', even if the bureaucracy is such that they are no so marked.Electrical accessories are not designed to IEC appliance standards and hence won't be assigned an appliance class. In practice though I would say a plastic accessory competently installed does provide similar protection to a class 2 appliance.
Nor do I, but it is that suggestion that led Sunray to be shocked that I was suggesting one should ignore the MIs which said that the Class I item "must be earthed".I do not disagree. On the contrary, I do not think it should be 'earthed' ... Hence, in reply to others, I do not think the item's metal parts should be 'bonded'.
Yes, but surely, for the isolated supply there is no earth.Nor do I, but it is that suggestion that led Sunray to be shocked that I was suggesting one should ignore the MIs which said that the Class I item "must be earthed".
Well, as you have said, this supposed 'earth' would not have achieve the function of a CPC.However, as you will have seen, I then thought a little more, and wondered whether this Class I item (which I had not earthed), which presumably did not have adequate 'double/reinforced' insulation to qualify it as Class II would theoretically be regarded as 'safe' to use with a floating supply at all.
Quite so - why not see if you can alleviate some of Sunray's 'shock' at the suggestion that one might ignore the "must be earthed" instruction in MIs when the supply is floatingYes, but surely, for the isolated supply there is no earth. That is, no path back to the supply either through the wiring or the planet. Isn't that the point and purpose of isolated supplies?
What hazards?
If one had a 240V battery (or generator I suppose) running a single appliance then surely connecting the appliance metal case to the house supply earth would only introduce hazards to the appliance and user?