isolator in bathroom

Discussion in 'Electrics UK' started by jeepster, 19 Dec 2010.

  1. jeepster

    jeepster

    Joined:
    19 Nov 2006
    Messages:
    60
    Thanks Received:
    0
    Location:
    Derbyshire
    Country:
    United Kingdom
    hi all, had extension buildt lastyear / begining of this year.I am doing the finishing off, ie tiling, decorating, new skirting etc. 8-10hours at weekends.

    In the new bathroom we have had an extractor fitted, its approx 450mm horizontally and 2.3m vertically from the end of the bath. this is one of the 12volt ones. inside zone 2.


    Anyhow, just inside 600mm from the end of the bath, at the same height they fitted an isolator switch for the fan.
    all of the electrics are protected by an rcd, should i get the electrcian to come back and move the isolator or is it ok where it is a present. alternatively could they fit a pull cord as an isolator.

    the fan is a vent axia 12volt model with humidity control so i guess they could have fitted it to the pull switch for the light.

    any comments from qualified electricians would be appreciated. cheers
     
  2. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    14,275
    Thanks Received:
    1,256
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    In zone 2:
    switchgear. accessories incorporating switches or socket-outlets shall not be installed with the exception of:
    (i) switches and socket-outlets of SELV circuits, the safety source being installed outside zones 0. 1 and 2. and
    (ii) shaver supply units complying with BS EN 61558-2-5.
    Except for SELV socket-outlets complying with Section 414 and shaver supply units complying with BS EN 61558-2-5,
    socket-outlets are prohibited within a distance of 3 m horizontally from the boundary of zone 1.

    So answer is simple low voltage (230v) switch is not allowed in zone 2.

    PS Zone 2 is limited by:
    (i) the finished floor level and the horizontal plane corresponding to the highest fixed shower head or water outlet or the horizontal plane lying 2.25 m above the finished floor level, whichever is higher.

    Are you sure it is zone 2?
     
  3. tonyelectric

    tonyelectric

    Joined:
    1 Dec 2010
    Messages:
    310
    Thanks Received:
    28
    Location:
    Southampton
    Country:
    United Kingdom
    Have the switch moved outside zones if it is actually within, ceiling mounting of fan isolator is not unusual (if permitted by zoning dimensions) or move switch out of bathroom to landing.

    You cannot have a pull isolator on most fans because the isolator used is a 3 pole one to switch the permanent and switched live and the neutral.
     
  4. jeepster

    jeepster

    Joined:
    19 Nov 2006
    Messages:
    60
    Thanks Received:
    0
    Location:
    Derbyshire
    Country:
    United Kingdom
    hi thanks for the info, the bottom of the switch is just inside 225, so will ask him to come back and move it.

    to be fair we are changing the layout of the bathroom so its not the electricians fault. will ask hi to put it above the basin at 225 or higher, i believe that is ok.
     
  5. GaryMo

    GaryMo

    Joined:
    3 Jul 2007
    Messages:
    4,114
    Thanks Received:
    162
    Location:
    Manchester
    Country:
    United Kingdom
    Is that 2.25M from the finished floor level or from the bottom of the bath?
     
  6. jeepster

    jeepster

    Joined:
    19 Nov 2006
    Messages:
    60
    Thanks Received:
    0
    Location:
    Derbyshire
    Country:
    United Kingdom
    hi, could he replace the isolator switch with a blanking plate ? without a switch.

    all of the extension electrics go through a rcd which i guess anyone working on one of the circuits would switch off anyway.
     
  7. DetlefSchmitz

    DetlefSchmitz

    Joined:
    17 Aug 2010
    Messages:
    1,707
    Thanks Received:
    213
    Country:
    United Kingdom
    I think personally I would invoke "de minimus ne curat lex", as we say in Germany.
     
  8. ELZ4742

    ELZ4742

    Joined:
    22 Jan 2007
    Messages:
    558
    Thanks Received:
    16
    Location:
    Oxford
    Country:
    United Kingdom
    nope, needs local isolation ;)
     
  9. dingbat

    dingbat

    Joined:
    29 Sep 2003
    Messages:
    2,846
    Thanks Received:
    68
    Location:
    West Midlands
    Country:
    United Kingdom
    Regulation number, please?
     
  10. riveralt

    riveralt

    Joined:
    4 Jan 2004
    Messages:
    4,020
    Thanks Received:
    597
    Country:
    United Kingdom
    134.1.1
     
    • Thanks Thanks x 1
  11. xr4x4

    xr4x4

    Joined:
    1 Oct 2009
    Messages:
    3,159
    Thanks Received:
    290
    Location:
    Hampshire
    Country:
    United Kingdom
    i thought you only needed a iso switch for a bathroom fan if there is no window?

    ie you need the lights on to see.
     
  12. ELZ4742

    ELZ4742

    Joined:
    22 Jan 2007
    Messages:
    558
    Thanks Received:
    16
    Location:
    Oxford
    Country:
    United Kingdom
    building regs require a fan if there is no window.
    there is no reg to say you have to have a light in any room.
     
  13. xr4x4

    xr4x4

    Joined:
    1 Oct 2009
    Messages:
    3,159
    Thanks Received:
    290
    Location:
    Hampshire
    Country:
    United Kingdom
    the question was, do you need a isolator switch for a bathroom fan, if the room has a window.
     
  14. ELZ4742

    ELZ4742

    Joined:
    22 Jan 2007
    Messages:
    558
    Thanks Received:
    16
    Location:
    Oxford
    Country:
    United Kingdom
    on the basis most iso switches would be outside the bathroom, it would be a bit daft ;)
     
  15. GaryMo

    GaryMo

    Joined:
    3 Jul 2007
    Messages:
    4,114
    Thanks Received:
    162
    Location:
    Manchester
    Country:
    United Kingdom
    Your first port of call would be the MI.
     