jeepster
hi all, had extension buildt lastyear / begining of this year.I am doing the finishing off, ie tiling, decorating, new skirting etc. 8-10hours at weekends.
In the new bathroom we have had an extractor fitted, its approx 450mm horizontally and 2.3m vertically from the end of the bath. this is one of the 12volt ones. inside zone 2.
Anyhow, just inside 600mm from the end of the bath, at the same height they fitted an isolator switch for the fan.
all of the electrics are protected by an rcd, should i get the electrcian to come back and move the isolator or is it ok where it is a present. alternatively could they fit a pull cord as an isolator.
the fan is a vent axia 12volt model with humidity control so i guess they could have fitted it to the pull switch for the light.
any comments from qualified electricians would be appreciated. cheers