No Neutral

Discussion in 'Electrics UK' started by mjtefc9, 8 Nov 2019.

  1. mjtefc9

    mjtefc9

    Joined:
    10 Oct 2014
    Messages:
    102
    Thanks Received:
    0
    Location:
    Liverpool
    Country:
    United Kingdom
    Hi all,

    I fitted an outside socket, all worked all ok, it was just taken from a socket inside.

    I got a belt from the front of the inside socket after it was fixed back and the juice on.. which had me baffled as it all worked perfect. I put my socket tester in the inside socket all ok... outside socket flashed up live earth reverse..

    Anyway took the front of both sockets and the neutral to from the outside socket to the inside had sheared of in the terminal when I'd forced the metal faceplate back.. so all rectified and working great... no more belts!

    My question is, why didn't it trip to stop me getting a belt?
     
  2. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    4,987
    Thanks Received:
    354
    Location:
    London
    Country:
    United Kingdom
    Why didn’t what trip? A MCB trips on overload. A broken neutral does not cause an overload. A RCD trips on unbalance. A broken neutral does not cause unbalance.
     
  3. mjtefc9

    mjtefc9

    Joined:
    10 Oct 2014
    Messages:
    102
    Thanks Received:
    0
    Location:
    Liverpool
    Country:
    United Kingdom
    Okay... so the Neutral caused arcing? Is that why I got a belt?
     
  4. Risteard

    Risteard

    Joined:
    18 Jun 2010
    Messages:
    1,842
    Thanks Received:
    124
    Location:
    Derry, Ireland
    Country:
    Ireland
    The word is IMBALANCE.
     
  5. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    41,731
    Thanks Received:
    2,615
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Sigh
     
    • Like Like x 2
  6. DetlefSchmitz

    DetlefSchmitz

    Joined:
    17 Aug 2010
    Messages:
    1,707
    Thanks Received:
    213
    Country:
    United Kingdom
    First question would be why didn't the earth to the front plate prevent this shock?
     
    • Like Like x 2
  7. mjtefc9

    mjtefc9

    Joined:
    10 Oct 2014
    Messages:
    102
    Thanks Received:
    0
    Location:
    Liverpool
    Country:
    United Kingdom
    Yes..this

    It's all wired correctly? ‍♂️ fly lead to the back box.. and the screws also acting as an earth

    I thought it would trip the breaker aswell?
     
  8. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    21,906
    Thanks Received:
    2,018
    Location:
    Bedfordshire
    Country:
    United Kingdom
    If it was wired correctly then the metal front plate would have been Earthed and hence 99% unlikely to be able to give you a shock.


    No. you got a shock because the Live conductor was making contact with the un-Earthed front plate.

    It might be that there is a fault elsewhere and the Earth conductor has been connected to Live somewhere else in the house ( the other 1% )
     
  9. mjtefc9

    mjtefc9

    Joined:
    10 Oct 2014
    Messages:
    102
    Thanks Received:
    0
    Location:
    Liverpool
    Country:
    United Kingdom
    But that wasn't the case.. the lives are all terminated correctly its was just a broken neutral, which when corrected meant everything was fine.? So your saying the broken neutral from the exterior socket wouldn't cause a shock?
     
  10. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    21,906
    Thanks Received:
    2,018
    Location:
    Bedfordshire
    Country:
    United Kingdom
    Yes
     
  11. mjtefc9

    mjtefc9

    Joined:
    10 Oct 2014
    Messages:
    102
    Thanks Received:
    0
    Location:
    Liverpool
    Country:
    United Kingdom
    Ok, well the live conducter wasn't touching the faceplate and this was the only fault..

    Thank you for your help though
     
  12. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    4,987
    Thanks Received:
    354
    Location:
    London
    Country:
    United Kingdom
    Which breaker? Read my post 2.
     
  13. DetlefSchmitz

    DetlefSchmitz

    Joined:
    17 Aug 2010
    Messages:
    1,707
    Thanks Received:
    213
    Country:
    United Kingdom
    There was something seriously wrong, and it would be foolish not to find out what, as you haven't fixed it. I would make some measurements using a multimeter and a long wire to a known good earth.
     
    • Like Like x 1
  14. mjtefc9

    mjtefc9

    Joined:
    10 Oct 2014
    Messages:
    102
    Thanks Received:
    0
    Location:
    Liverpool
    Country:
    United Kingdom
    Thanks pal,

    It's a new build and never had any issues, the socket itself was also never an issue this only seems to of occurred when I added this exterior socket. I have put the socket tester in both outlets now and they read perfect.

    I'll get the Multimeter from work and do some testing..
     
  15. Keithmac

    Keithmac

    Joined:
    10 Oct 2017
    Messages:
    1,157
    Thanks Received:
    181
    Country:
    United Kingdom
    I had a break in our lighting circuit earth, been like it when we moved in but only became apparent 10 years later when I fitted metal light switches.

    The earth was disconnected but picked up 70v due to being in the same cable as the live.

    You should not have got a belt from the socket with a good earth, there is something wrong somewhere. Is there any provision for an earth wire to the face plate?.
     
    • Thanks Thanks x 1