Plug Socket Question

Joined
5 Nov 2008
Messages
560
Reaction score
20
Country
United Kingdom
I have purchased MK Logic Plus sockets for my house.
All sockets are being replaced as and when I finish decorating rooms.

My question is and it may be silly: From screwfix why do the MK double sockets have one earth point in the centre but the MK single sockets have two earth points one either end?

Is there any technical advantage to having the two earth terminals?

Do MK actually do a logic plus double with 2 earth points?

Many Thanks
 
Sponsored Links
Look on MK's website-all their products are available on there to view.

From a technical point of view, 2 earth terminals on one socket outlet is required for circuits that require high integrity earthing. HIE is required where a protective conductor current is expected to be over 10mA.

This isnt something you need to worry about in the average domestic setup though.
 
MK logic plus sockets are available with the dual earth terminals, but they are more expensive, and not usually required in a domestic environmet, so are not generally available in the DIY sheds.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top