It means switchgear assemblies that are similar to a CU.So what does "and similar switchgear assemblies" in 421.1.201 mean?Your box full of raspberry pies, arduinos, etc is not within the scope of the standard for switchgear and controlgear assemblies.
If the scope of BS EN 61439-3 is relevant to 421.1.201 does that mean:
a) We can use BS EN 61439-3 as a guide to what "non-combustible" means?
b) I could indeed assemble my enclosure, MCBs, RCBOs, RCDs, switches, E & N distribution blocks etc and use it in place of a CU and not have to worry about 421.1.201 because that distribution board is not similar to a CU?
a) You can. Whether that is sufficient or not, I don't know. I thought I did, but...
b) If you assembled an enclosure with components that are switchgear, and are typically used as components of a CU, then you've built something that is similar to a CU, or perhaps is a CU.