Rcd or not

Joined
13 Nov 2004
Messages
882
Reaction score
12
Location
Berkshire
Country
United Kingdom
A small job of extending a ring main in an industrial canteen to include 1x socket.
Surface mounted earthed galv conduit ocpd 3036 no rcd insight.
RCD the circuit at source or just use an SRCD?
 
Either is acceptable, it is up to you and the customer to decide. Personally I'd lean towards doing the whole circuit.
 